how to check the stabilty test for generator differential
protection
Answer / raghavendran
Checking of the pickup and dropout value
When checking the pickup value, the analogue input signals
of the single phase alternating test current have to be fed
to the relay via terminals.When testing the pickup value,
the alternating test current must first be lower than the
set pickup value.
Then the current will be increased until the relay picks up.
The value that can be read from the ammeter may not deviate
by more than ± 2.5% of the setting value. The tripping
values for the other current inputs should be checked
accordingly.
Function test
Disconnect all leads for adjusting the interposing C.T.s and
perform the following function test:
Load the generator with minimum 50% load. Assure that the
tripping of the generator C.B. does not cause un-wanted
damages (blackout).
To operate the differential relay use a shorting link
between one of the phase measuring sockets
and GND, e.g. connect Line to GND. The relay should trip
immediately. If no trip occurs, make sure
that the load current exceeds the set value.
| Is This Answer Correct ? | 0 Yes | 1 No |
Is the installation of the filter cloths necessary before spreading the gravels at the transformer yards?
how dia of wire and angles are calculated for overhead shielding wire to protect substation equipment from lightening strokes???
what is the step by step formula for calculating bus bar phase and neutral size of a panel board.suppose the incomer of panel board is 100A..???step by step answer please
i have gear oil pump with single phase motor.some time its motor starts running in reverse direction rather than forward direction...whats the reason behind this issue. 1- either capacitor is week? 2- or winding is week?
what is REF relay?
Write a note on Treatment for electric shock.
what is the full form of MEMO? name of memo train.
we have one oven for 12 zone we are installed ir lamp in oven we control load from thyrister and 0 to 5vdc so our zone no 8 getting bright in fraction of second so what we do.. Please answer
As the one point of eac phase winding is connected to each other in satr connction. Even if that at distribution side collesion of two diff phases result in to blast. Why?
out of all machines which have highest efficiency and why?
what shall be no load voltage of 132/33 kV transformer ? is it 33 kv of 34.5 kV
Why hydropower stations are preferred solution for meeting peak loads in grids?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)