how to check the stabilty test for generator differential
protection
Answer / raghavendran
Checking of the pickup and dropout value
When checking the pickup value, the analogue input signals
of the single phase alternating test current have to be fed
to the relay via terminals.When testing the pickup value,
the alternating test current must first be lower than the
set pickup value.
Then the current will be increased until the relay picks up.
The value that can be read from the ammeter may not deviate
by more than ± 2.5% of the setting value. The tripping
values for the other current inputs should be checked
accordingly.
Function test
Disconnect all leads for adjusting the interposing C.T.s and
perform the following function test:
Load the generator with minimum 50% load. Assure that the
tripping of the generator C.B. does not cause un-wanted
damages (blackout).
To operate the differential relay use a shorting link
between one of the phase measuring sockets
and GND, e.g. connect Line to GND. The relay should trip
immediately. If no trip occurs, make sure
that the load current exceeds the set value.
| Is This Answer Correct ? | 0 Yes | 1 No |
Transformer Secondary maximum current (max. load)
I had finished D.E.E.E at 2004,I wish to take C license.I am working pvt company HT supply but my professional certificate was missing.I have diploma & course completed certificate.without professinel may I got c license?.pls guide me.
why sec of ct should be kept shorted
what is the function of AVR in generator? how the generator maintain the frequency while varies the load?
what is dielectric heating
Safety of dry type transformer
what is meant by power and distribution transformer ?
2- What are the percentages between excitation currents in phase (R, S and T) in ∆ and Ỵ connections in excitation Current test in transformers?
my diploma certificate in my higher education college
Can the efficiency of transformer be measured with the help of wattmeter readings taken at primary and secondary side? Support the answer.
why 3phase is 440v but where as we get phase voltage 220v,we have to get 220*3=660v.can u pleas give in detailed
How we check vector group for a Dyn1 transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)