Answer / karthik
Megger is used to test the resistance/insulation capacity
between two conductors be it
(*) Phase and neutral
(*) Line to ground.
(*) Phase to phase
For testing using megger
(*) Connect one terminal to the phase and other terminal to
neutral/ground for testing line to ground resistance.
(*) Connect one terminal to phase and other terminal to
another phase in case of phase to phase resistance.
All the nominal value of resistance must be greater than
atleast 1Mohm.
| Is This Answer Correct ? | 21 Yes | 0 No |
What is the normal phase difference between the voltage and the no-load current in a transformer?
where can i get the previous years question papers for APGENCO exam.
Why 66KV is step down to 11KV and then 433v, not directly 66KV to 433v ?
what is the lightning arrester rating for 3.3kv system voltage
What is the difference between line Distance protection and Line Earth Fault Protection?
What are the tests to be taken on a transformer and generator?
what is the formula of starting current of 3phase and 1 phase motor???
What are the reasons for the parallel operation of transformers?
why the substation require din electrical system?
What is inductance?
what is allowable current flows from phase to ground with out tripping the breaker
Regarding units, for voltage we are denoting Volts as V but in case of current we are not denoting Ampere as A instead as I..Why..? Any technical reason for this..?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)