Answer / sudheer

one ton refrigeration ton(TR)was defined as the heat
absorved by the one ton of ice (2000 pounds) causing it to
melt completely by the end of one day ( 24 hours).

1 RT= 2000 POUNDSX 144 BTU per pound / 24 hours
= 12000 BTU'S per hour
= 200 BTU/min
= 3.517 kj/s
= 3.517 kw
= 3516 watts
= 4.72 HP
so, TR= 3.517 KW

Is This Answer Correct ?    355 Yes 44 No

1 tr is equal to how many Kw .is there any specific formula for this to get the result ...

Answer / kusum

1 Tr = 3.517 KW

Is This Answer Correct ?    157 Yes 16 No

1 tr is equal to how many Kw .is there any specific formula for this to get the result ...

Answer / mahendrakumar.s

1 RT= 2000 POUNDSX 144 BTU per pound / 24 hours
= 12000 BTU'S per hour
= 200 BTU/min
= 3.517 kj/s
= 3.517 kw
= 3516 watts
= 4.72 HP
so, TR= 3.517 KW

Is This Answer Correct ?    163 Yes 24 No

1 tr is equal to how many Kw .is there any specific formula for this to get the result ...

Answer / faizaz

1 TR = 3.517 KW

Is This Answer Correct ?    79 Yes 15 No

1 tr is equal to how many Kw .is there any specific formula for this to get the result ...

Answer / arif

500 TR is equal to how many kw.is there any spesicific
formula for this to get the result.

Is This Answer Correct ?    78 Yes 25 No

1 tr is equal to how many Kw .is there any specific formula for this to get the result ...

Answer / srinivas

1 kw is 1000 watts we no that
1 watt is 3.41 btu/hr

1x1000x3.41=3410 btu/hr

12000/3410 where 1TR=12000 btu/hr
=3.517

Is This Answer Correct ?    67 Yes 14 No

1 tr is equal to how many Kw .is there any specific formula for this to get the result ...

Answer / kumar

one ton refrigeration ton(TR)was defined as the heat
absorved by the one ton of ice (2000 pounds) causing it to
melt completely by the end of one day ( 24 hours).

1 RT= 2000 POUNDSX 144 BTU per pound / 24 hours
= 12000 BTU'S per hour
= 200 BTU/min
= 3.517 kj/s
= 3.517 kw
= 3516 watts
= 4.72 HP
so, TR= 3.517 KW

Is This Answer Correct ?    44 Yes 7 No

1 tr is equal to how many Kw .is there any specific formula for this to get the result ...

Answer / david joson

The TR for the ACCU is determined by its efficicient Coefficient of regrigeration or the (COP) Coefficient of Performance. It ranges from 1.5 to 2 max value depending on its voltages. Thus 1TR=1x1.5x746=1119 watts or 1.5 hp

Is This Answer Correct ?    6 Yes 1 No

1 tr is equal to how many Kw .is there any specific formula for this to get the result ...

Answer / nabil babili

1RT=3.517 KW=200 BTU=4.72HP
kW=56.8 BTU
HP=42.3 BTU

Is This Answer Correct ?    3 Yes 2 No

1 tr is equal to how many Kw .is there any specific formula for this to get the result ...

Answer / ramkrishna

1ton = 1000*latent heat/(24*60)=232kj/min
in practice 1 ton = 210kj/min

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Which one is easy to control AC or DC Machine?

2 Answers   BARC,


what is power factor ?

3 Answers  


iam completed my DEEE in eillm university. can i get the c licence in tamilnadu its possible or not

1 Answers  


what should be the value of helathy insulation b/w two cores of LT cable.

2 Answers  


What is the universal motor?

0 Answers  






what is the earth current,reverse power,electrical trip generator short circuit,low voltage, high voltage please discribe me

0 Answers  


DESCRIBE THE CONSTRUCTION ANDOPERATION OF BELT CONVEYORS AND SCR CONVEYORS , DRAW NEAT SKETCHES

0 Answers  


Is it possible to protect 3phase overload and earth fault of the 3phase system using two CT's.

0 Answers  


Which motor has more efficiency ;Synchoronous or Induction motor ?

4 Answers   TATA,


What is the vector group of a transformer,how can it be found out?

0 Answers   Jindal,


WE know that for Inductor X=2pifL,In DC f=0,then X=0 so,V=IX=0;But In the DC excitation of rotor of AC generator,DC motor field coil which coils are inductor so why does not applying DC voltage short the rotor coil of AC generator and field coil of motor?If it would then DC source might be damaged but it is not happened. Why does the strand conductor of Electrical power transmission line make twist?

0 Answers  


block diagram of 2 ups system connected in parallel mode?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)