1 tr is equal to how many Kw .is there any specific formula
for this to get the result .
Answer Posted / sudheer
one ton refrigeration ton(TR)was defined as the heat
absorved by the one ton of ice (2000 pounds) causing it to
melt completely by the end of one day ( 24 hours).
1 RT= 2000 POUNDSX 144 BTU per pound / 24 hours
= 12000 BTU'S per hour
= 200 BTU/min
= 3.517 kj/s
= 3.517 kw
= 3516 watts
= 4.72 HP
so, TR= 3.517 KW
| Is This Answer Correct ? | 355 Yes | 44 No |
Post New Answer View All Answers
for 5KW resistive load can anyone please suggest me whether to go for UPS/Inverter or Generator depending upon cost calulations
why the colour of insultor stack , petticoat is brown. Is it has some technical reason.
Why does the radius of armature is less than the radius of pole shoe?
What is the necessary and sufficient condition for stability.
what is ground fault in ACB?
Dear Brother can u tell the proper size selection of cable & the fault level calculation of braker, busbar etc. pls mail me at azeemk30@gmail.com
May I know how much values to be set for earth fault, over current and short circuit values at 11kv side? I have 11kv van 1250amps rating. Present it's taking load 80amps?
Is there any question in the name of Static Switch in UPS??
in ACB breaker requireding 3200Amps. buscoupler getting OFF mode and again it reset and getting normal position give me a required answer?
State the methods of improving power factor?
How to calculate the size of earth cable to earth the neutral of UPS ?
How many devices can be connected in one zone of FACP
what is the power rating of CPU, CRT type moniter, LCD type moniter,scanner Approx.
What si the d/f b/w KVA & KWH, kvarh & kvar, kwh & kvar phase voltage & line voltage
working principles of cf lamp,incandescentlamp and f lamp?