For Synchronisation of DG Sets Sometimes we people use NIC
(Neutral Isolation Contactor) Instead of 4-pole ACB or any
switchgerar..Please guide me why is it so????
Answers were Sorted based on User's Feedback
Answer / srikanth shreenidhi
Whenever DGs are paralled & synchronised one should have a
common neutral.If neutral of one generator fails
automatically the neutral of other dg sets which is on a
common bus takes over.Whereas if the DG has a 4 pole
breaker and neutral fails it will be impossible for the
system to continue as all the dg sets will have a switched
neutral.
Secondly in case of neutral/contactor failure the user will
have to change only the contactor instead of the whole
breaker
However when only one DG set is used we always go with 4
pole breaker.
| Is This Answer Correct ? | 16 Yes | 8 No |
Answer / vinod
when a DG set is started and as dg voltage is building up it is necessary to connect the lowest potential point of generator first with the system which it is to be feed, that is the neutral as first. then the breaker can be closed if the set is required to be parallel first. the reason is the system which the DG is intended to supply may have a neutral potential which can be at a different potential other than the DG. so in order to establish a common neutral NIC is used. if NIC is not there and DG neutral is always solidly connected to the BUS then grounding impedance of the whole system is reduced and in turn fault in system can lead to a higher fault current.
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / muniraja1283@rediffmail.com
above said subject full very satisfactury
| Is This Answer Correct ? | 3 Yes | 4 No |
Answer / zuber ahamed
Whenever DGs are paralled & synchronised one should have a
common neutral.If neutral of one generator fails
automatically the neutral of other dg sets which is on a
common bus takes over.Whereas if the DG has a 4 pole
breaker and neutral fails it will be impossible for the
system to continue as all the dg sets will have a switched
neutral.
Secondly in case of neutral/contactor failure the user will
have to change only the contactor instead of the whole
breaker
However when only one DG set is used we always go with 4
pole breaker.
| Is This Answer Correct ? | 1 Yes | 5 No |
can we calculate the diameter of the cable by its cross section?
what is the function of RMU?
why capacitor using the induction motor?
Explain the propagation of harmonics in the network and influence of phase angle of harmonics.
What is the arc. I saw word arc in between sf6 & vcb brakers
How to calculate load taken by a cable?
design a 3 bit synchronous and asynchronous counter using T- flipflop
What are the uses of lead compensator?
What is maximum AC & DC transmission voltage in India? and where?
Why delta connected motors are used normally.
What is the direction of rotation of blades in a table fan and in a ceiling fan ?
If single phase having 220v so why 3phase is440v.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)