For Synchronisation of DG Sets Sometimes we people use NIC
(Neutral Isolation Contactor) Instead of 4-pole ACB or any
switchgerar..Please guide me why is it so????
Answers were Sorted based on User's Feedback
Answer / srikanth shreenidhi
Whenever DGs are paralled & synchronised one should have a
common neutral.If neutral of one generator fails
automatically the neutral of other dg sets which is on a
common bus takes over.Whereas if the DG has a 4 pole
breaker and neutral fails it will be impossible for the
system to continue as all the dg sets will have a switched
neutral.
Secondly in case of neutral/contactor failure the user will
have to change only the contactor instead of the whole
breaker
However when only one DG set is used we always go with 4
pole breaker.
| Is This Answer Correct ? | 16 Yes | 8 No |
Answer / vinod
when a DG set is started and as dg voltage is building up it is necessary to connect the lowest potential point of generator first with the system which it is to be feed, that is the neutral as first. then the breaker can be closed if the set is required to be parallel first. the reason is the system which the DG is intended to supply may have a neutral potential which can be at a different potential other than the DG. so in order to establish a common neutral NIC is used. if NIC is not there and DG neutral is always solidly connected to the BUS then grounding impedance of the whole system is reduced and in turn fault in system can lead to a higher fault current.
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / muniraja1283@rediffmail.com
above said subject full very satisfactury
| Is This Answer Correct ? | 3 Yes | 4 No |
Answer / zuber ahamed
Whenever DGs are paralled & synchronised one should have a
common neutral.If neutral of one generator fails
automatically the neutral of other dg sets which is on a
common bus takes over.Whereas if the DG has a 4 pole
breaker and neutral fails it will be impossible for the
system to continue as all the dg sets will have a switched
neutral.
Secondly in case of neutral/contactor failure the user will
have to change only the contactor instead of the whole
breaker
However when only one DG set is used we always go with 4
pole breaker.
| Is This Answer Correct ? | 1 Yes | 5 No |
is all the servo motors having brake?please specify which servo motors having brake for stop on position and which are not.
hi frnds...pls send me aptransco previous papers .....pls..pls,,,(madhar.rocking@gmail.com)and suggest me some websites
What are Line losses and how can be it minimized/controlled.?
The iron loss in a 100kva transformer is 1 kw and full load copper losses are 2 kw, then what is maximum efficiency occure at a load?
Dear all, I just want to ask an expert on this forum for some insights. For the magnetic balance test, when applied voltage on a Delta-Star transformer e.g. Dyn11, the following relationships apply for HV side: 1. H1-H2 = H2-H3 H3-H1 2. H2-H3 = H3-H1 H1-H2 3. H3-H1 = H1-H2 H2-H3 For the LV side also: 4. X1-X0 = X2-X0 X3-X0 5. X2-X0 = X3-X0 X1-X0 6. X3-X0 = X1-X0 X2-X0 Is there a similar pattern for Y-d, Y-Y, D-d? And how about Y-z, D-z, Z-y transformers? I've tested a YNzn5 transformer and for LV side I don't see the pattern. In this particular case I got for LV side the following (see values below): H1-H0 H2-H0 H3-H0 X0-X1 X0-X2 X0-X3 128.0 119.9 7.2 29.2 13.3 15.8 70.7 128.4 59.2 23.4 22.0 3.6 7.2 120.1 128.1 13.4 29.3 15.8 What is the relationship here for LV? For row 1 I see the relationship, for row 3 I also see but it's shifted, but for row 2 I don't see such relationship. Any suggestions, answers, someone?
How to convert a two phase power into a three phase power in induction machine?
why we are called the 4-20ma transducer,not 0-20 ma transducer??
should %impedance be high or low in a power transformer? if so why?
How we can calculate the Amps for the cable Ex:- For 1sqmm wire how many amps we can draw (calculation)
how we can calculate chiller required ampear?
whether choke act as a voltage regulator in tubelight or not?
I am going to appear for the RRB Chennai Section Engineer online exam. Please send me the question papers from 2001 to date to my mail id: vsujith_rajan@yahoo.co.in
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)