Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


For Synchronisation of DG Sets Sometimes we people use NIC
(Neutral Isolation Contactor) Instead of 4-pole ACB or any
switchgerar..Please guide me why is it so????

Answers were Sorted based on User's Feedback



For Synchronisation of DG Sets Sometimes we people use NIC (Neutral Isolation Contactor) Instead of..

Answer / srikanth shreenidhi

Whenever DGs are paralled & synchronised one should have a
common neutral.If neutral of one generator fails
automatically the neutral of other dg sets which is on a
common bus takes over.Whereas if the DG has a 4 pole
breaker and neutral fails it will be impossible for the
system to continue as all the dg sets will have a switched
neutral.
Secondly in case of neutral/contactor failure the user will
have to change only the contactor instead of the whole
breaker

However when only one DG set is used we always go with 4
pole breaker.

Is This Answer Correct ?    16 Yes 8 No

For Synchronisation of DG Sets Sometimes we people use NIC (Neutral Isolation Contactor) Instead of..

Answer / vinod

when a DG set is started and as dg voltage is building up it is necessary to connect the lowest potential point of generator first with the system which it is to be feed, that is the neutral as first. then the breaker can be closed if the set is required to be parallel first. the reason is the system which the DG is intended to supply may have a neutral potential which can be at a different potential other than the DG. so in order to establish a common neutral NIC is used. if NIC is not there and DG neutral is always solidly connected to the BUS then grounding impedance of the whole system is reduced and in turn fault in system can lead to a higher fault current.

Is This Answer Correct ?    9 Yes 1 No

For Synchronisation of DG Sets Sometimes we people use NIC (Neutral Isolation Contactor) Instead of..

Answer / muniraja1283@rediffmail.com

above said subject full very satisfactury

Is This Answer Correct ?    3 Yes 4 No

For Synchronisation of DG Sets Sometimes we people use NIC (Neutral Isolation Contactor) Instead of..

Answer / zuber ahamed

Whenever DGs are paralled & synchronised one should have a
common neutral.If neutral of one generator fails
automatically the neutral of other dg sets which is on a
common bus takes over.Whereas if the DG has a 4 pole
breaker and neutral fails it will be impossible for the
system to continue as all the dg sets will have a switched
neutral.
Secondly in case of neutral/contactor failure the user will
have to change only the contactor instead of the whole
breaker

However when only one DG set is used we always go with 4
pole breaker.

Is This Answer Correct ?    1 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

What is the effect on in Zone and out zone fault if Phase side CT is Vk/2<30 mA and Neutral side is CT is Vk/4<30 mA for Transformer REF protection

0 Answers   ABB,


why insulation cost is more in underground cable than in overhead line?

2 Answers  


what will happen if neutal in AC ckt will get open

3 Answers  


When lag/lead/lag-lead compensation is employed?

0 Answers  


State four criteria's for selection of site for nuclear power station.

1 Answers  


what are the types of cooling systems used in motors?

2 Answers  


How to make vector group test of transformer?

2 Answers  


how to find transformation ratio of squirrel cage induction motor

0 Answers   BITM, WER,


What is DC power factor??

2 Answers   HCL,


when we start the tube light, then it takes initially 1100 volt, after glow it takes 120 volt?(when we give 220 volt a.c.)

3 Answers  


how system voltage affect the power factor or vice-versa.

4 Answers  


can we use HT cables for LT power supply ?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)