how to calculate cable size by amp
Answers were Sorted based on User's Feedback
Answer / m l sharma
When we calculate the cable size by Amp then we consider the type of load (inductive,resistive, capacitive)& voltage drop.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / ayman
by knowing the load current and voltage and the length
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pk
It depends on the length from source to load, maximum permissible loss and thermal capacity of insulation.
Resistance = Rho x Length / Cross Sectional Area
Voltage Drop = Current in the wire x Resistance
The resistance of the wire leads to voltage drop
Depending on how much voltage drop is permissible at the load the area should be chosen appropriately
The second factor is heat produced.
Energy Loss = heat produced = I^2 x R.
This will lead to a temperature increase. The insulation should be able to handle this rise. Also the losses should be as low as possible to improve efficiency.
This is the theory. Thumb rules of 3-5 Amperes per sqmm are prevalent in the industry
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ravinder paul
what is the size of 7/14,7/16,37/16 cables in mm
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / farhat ali
cable length is 6 Meters load is 152 Amp. 3 phase 110 v.
what size cable is used for that
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / suthan prabhu
for copper cable 1Sqmm can carry 1.92 Amps .
Is This Answer Correct ? | 18 Yes | 32 No |
why we use delta connection in transformer
if we use contactor & MCCB both in a feeder.in this feeder rating of contactor is higher or lower or same of MCCB rating & why?
what are the safety measures of induction motor?
what are the reasons of low voltage during start the DG?
I AM DOIN MY 3RD YEAR IN ELECTRICAL ELECTRONICS. PLEASE SUGGEST WHAT DO I DO NEXT AFTER MY B.E? AND I WANT TO GET INTO ANY PSU IS DER ANY EXAMS PLASE SUGGEST EVEN THAT.
What is the maxvoltage drop allowed at any healthy joint at full load ?
why generation of electricity in low value voltage
how do we calculate length of starting time and repeated starting of a direct online starter?
What is the capacitance values of 132,220,400 & 765 kV current transformer
what is the practical application of full adder circuit?
0 Answers College School Exams Tests,
Wat is the best to use in a generator a 6.5kva or a 7 kw
why we measure ouput of transformers in kva.