what is High resistance grounding and whatis the criteria
for the selection of High resistance grounding
Answer / akshay chauhan
High Resistance Grounding (HRG) is a method where high resistance is connected between a system's neutral point and ground to limit ground fault current, usually to less than 10 amps, allowing the system to continue operating during a single ground fault while protecting equipment.
Selection Criteria:
System Voltage: Suitable for low (up to 600V) and medium-voltage (up to 15kV) systems.
Fault Current Limit: Typically limits fault current to 5-10 amps.
Neutral Availability: Requires an accessible neutral point (e.g., wye transformer).
System Continuity: Used where continuous operation during faults is critical.
Ground Fault Detection: Should include monitoring for fault identification.
Is This Answer Correct ? | 0 Yes | 0 No |
What are the effects to a distribution transformer rated 10Kv with ratio 10Kv/0.433Kv, 3phase 50hz for example but fed with power supply of 11Kv?
In ac which gas will be use?
What are the protections for HT Motors?
what are the types of transformers
Sir, Please tell me that how I will calculate the efficiency of rectifier. Because input is ac and output is dc. Is it right to put two unlike signal together.
Why distribution transformer secondary voltage is 0.433kV instead of 0.415kV.all other switchgear rating are 415 volt??
what is current
53 Answers Bio Enterprises, CLG, TCS,
can mini-curcuit supply MIL-tested transformer !
what is CT class? depending upon which it is classified?
What are the properties of a resistor?
can we run a motor rated 50Hz,415vac,1440RPM At higher speed then rated on name plate with the help of VFD /drive on long term basis.wheater it will effect the motor life
what is the importance of neutral in elctrical system?
4 Answers IOCL, Kharafi National,