Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why ELCB can't work if N input of ELCB do not connect to
ground?

Answers were Sorted based on User's Feedback



why ELCB can't work if N input of ELCB do not connect to ground?..

Answer / suresh kumar

ELCB is used to detect earth leakage fault. Once the phase
and neutral are connected in an ELCB, the current will flow
through phase and that much current will have to return
neutral so resultanr current is zero. Once there is a
ground fault in the load side, current from phase will
directly pass through earth and it will not return through
neutral through ELCB. That means once side current is going
and not returning and hence because of this difference in
current ELCB wil trip and it will safe guard the other
circuits from faulty loads. If the neutral is not grounded,
fault current will definitely high and that full fault
current will come back through ELCB, and there will be no
difference in current.

Is This Answer Correct ?    38 Yes 13 No

why ELCB can't work if N input of ELCB do not connect to ground?..

Answer / dayal varma

the main function of the ELCB is to trip the circuit when
ever the fault in earth ocuurs so it needs a ground
referance. other wise it will not work

Is This Answer Correct ?    23 Yes 6 No

why ELCB can't work if N input of ELCB do not connect to ground?..

Answer / chiss

Hi,all, i've got a problem with the understanding of ELCB,
may i know if only Red and yellow phase (2 wire of 3 phase)
connected to 4 pole ELCB? Does ELCB need a neutral to make
it work?

Is This Answer Correct ?    11 Yes 3 No

why ELCB can't work if N input of ELCB do not connect to ground?..

Answer / rayvandy

No, it doesnt need earth wire to be connected to elcb/rccb. But it is recommended to connect every electrical appliances in your house with earth wire/ground. When there is a leakage, the lccb will detect that current in the live wire is higher than current that returns to neutral wire through lccb. Because the two currents is not balance, lccb will cut off the electricity. For more info u can refer to this site: http://www.gcsescience.com/pme9.htm

Is This Answer Correct ?    9 Yes 2 No

why ELCB can't work if N input of ELCB do not connect to ground?..

Answer / mayuur

There is no need of connection to ground because there is two current pass which are passed in oppose direction so the flux in the coil has been nullyfied .     
And if u connected n terminal into ground there the relay trip immediatly

Is This Answer Correct ?    2 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what is the profesional board for electrical engineer what is thepast and during construction for electrical engineering

0 Answers  


DIFFERENCE BETWEEN TRANSFORMER AND CURRENT TRANSFORMER?

7 Answers  


its Kva and Kv are same?

3 Answers  


why VCB are not used in 132KV system(above 33KV system)

6 Answers   Al Ahleia,


Is there possible to Test Transformer for Overfluxing Capability. Or is there any firm who does Overfluxing Test on Transformer?

0 Answers  


can any one tell me the formula for calculating the power and unit consumpetion

9 Answers   Avalon,


In the UVR(Under Voltage Relay) there is a knob for the hysteresis setting. what is this setting? its threshold is given from 5% to 50%. please help me....

2 Answers  


Actually why the transformers ate rated in KVA.?

2 Answers   Torrent Pharma, XYZ,


why star point of HT motor not earthed?

0 Answers  


whenever any squirrel or a crow falls on the transformer input line then there is a big explosion and 440 volts of power is being discharged through the neutral line due to which appliances in off mode are also burned.we have earthing for the transformer as well as the bus bar chamber.why is it happening?

1 Answers  


in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 33v to 430.v.

18 Answers   Eaton, Siemens,


what modulation is used in landline telephone signals?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)