ELCB is used to detect earth leakage fault. Once the phase
and neutral are connected in an ELCB, the current will flow
through phase and that much current will have to return
neutral so resultanr current is zero. Once there is a
ground fault in the load side, current from phase will
directly pass through earth and it will not return through
neutral through ELCB. That means once side current is going
and not returning and hence because of this difference in
current ELCB wil trip and it will safe guard the other
circuits from faulty loads. If the neutral is not grounded,
fault current will definitely high and that full fault
current will come back through ELCB, and there will be no
difference in current.
| Is This Answer Correct ? | 38 Yes | 13 No |
Answer / dayal varma
the main function of the ELCB is to trip the circuit when
ever the fault in earth ocuurs so it needs a ground
referance. other wise it will not work
| Is This Answer Correct ? | 23 Yes | 6 No |
Answer / chiss
Hi,all, i've got a problem with the understanding of ELCB,
may i know if only Red and yellow phase (2 wire of 3 phase)
connected to 4 pole ELCB? Does ELCB need a neutral to make
it work?
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / rayvandy
No, it doesnt need earth wire to be connected to elcb/rccb. But it is recommended to connect every electrical appliances in your house with earth wire/ground. When there is a leakage, the lccb will detect that current in the live wire is higher than current that returns to neutral wire through lccb. Because the two currents is not balance, lccb will cut off the electricity. For more info u can refer to this site: http://www.gcsescience.com/pme9.htm
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / mayuur
There is no need of connection to ground because there is two current pass which are passed in oppose direction so the flux in the coil has been nullyfied .
And if u connected n terminal into ground there the relay trip immediatly
| Is This Answer Correct ? | 2 Yes | 0 No |
what is the profesional board for electrical engineer what is thepast and during construction for electrical engineering
DIFFERENCE BETWEEN TRANSFORMER AND CURRENT TRANSFORMER?
its Kva and Kv are same?
why VCB are not used in 132KV system(above 33KV system)
Is there possible to Test Transformer for Overfluxing Capability. Or is there any firm who does Overfluxing Test on Transformer?
can any one tell me the formula for calculating the power and unit consumpetion
In the UVR(Under Voltage Relay) there is a knob for the hysteresis setting. what is this setting? its threshold is given from 5% to 50%. please help me....
Actually why the transformers ate rated in KVA.?
2 Answers Torrent Pharma, XYZ,
why star point of HT motor not earthed?
whenever any squirrel or a crow falls on the transformer input line then there is a big explosion and 440 volts of power is being discharged through the neutral line due to which appliances in off mode are also burned.we have earthing for the transformer as well as the bus bar chamber.why is it happening?
in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 33v to 430.v.
what modulation is used in landline telephone signals?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)