what is the concept of star delta starter?
Answers were Sorted based on User's Feedback
Answer / gajanan
star delta starter is used to reduced starting current
taken by motor. for this first startor wdg made connect in
star and then in delta.
Is This Answer Correct ? | 47 Yes | 2 No |
Answer / senthil
for reducing the motor starting current,initially motor
will take 4to 5 times of full load current,If we use star
delta it will reduce 1.732times of its torque as well as
current will reduce,motor will get safe
Is This Answer Correct ? | 29 Yes | 6 No |
Answer / shyamkr
actually the main concept is to reduce the starting current.
initially stator windings are connected to the bus through
star connections it reduces the stating voltage to 1.732
times n hence the starting current.
after sometime ,when max.speed is achieved it has been delta
connected and the voltage applied at the terminals is equal
to phase voltage.
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / praful nandankar
Basically star delta starter is used to reduce the starting
current.When u'r connections are in star, the voltage is
reduced by 1/1.732 times.When the motor attains 80% of
speed, connections changed to delta.
praful nandankar
Is This Answer Correct ? | 6 Yes | 2 No |
The concept of star delta starter is to reduce the starting
current of motor. in star connection line voltage and
pahase voltage is same which is 230v.so srating current
normally reduced.
Is This Answer Correct ? | 9 Yes | 6 No |
Answer / gunnam santosh
for an induction motor at starting current is very high
speed is small so initially reduced current is applied.for
star connected winding phase voltage is root3 times the line
voltage and for delta current is root3 times the line current
so initial current can be reduced by using delta and then
star during starting of the motor
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / jagadisha.n. bmsit
At the starting motor needs high torque to reach rated speed
so it will required more flux to get that torque hence it
takes more current from the supply, but the winding
resistance is too low to withstand this current.
we know that
in star phase current = sqrt(line current)
In delta line current = phase current
So current is reduced by sqtt(3) times in star so motor is
first connect to star and then delta
Is This Answer Correct ? | 17 Yes | 16 No |
WHY ARMAD USE IN CABLE
what is the use of the puls transformer in UPS & how it works???????????
I find that underground strip-armoiured,4core,LT PVC cables in an earthed power distribution sytem are occasionly found in charred condition-with no trace of it except ash. Is this because of no proper earth connection/continuity (giving rising to high armour resistance)in the joint enroute or because of insufficient capability (again due to high armour resistance)of cable-armour to carry fault current or due to neglected /unprotected overloading of the cable or due to high armour currents caused by power thefts where only phase(s) are unauthorisely tapped & at the point of poer consumption earth terminal is established by burring underground a not so good earthing rod (or using an underground water pipe for the purpose)
why we have to do tan delta test of the transformer oil???
Explain how you intend to work under pressure to meet up with deadline target?
Working of microwave oven?
Whai isPCC and MCC Difference?
WILL SCHNEIDER MAKE ACB(MASTERPACT)TRIP ON REVERSE POWER?
what is the uses of C.V.T transformer in switch yard?
what will happen when excitation of a synchronous machine is suddenly reduce to zero when it is running at full load..??
What are the two segments of nyquist contour.
Using 11000V/433V,3 ph,50Hz,500 KVA, what is the maximum capacity of motor in KW that can be connected and started at a single moment? Also explain about any calculations and formulas used in deriving the same.