How we find the size of cable if we know the current
Answers were Sorted based on User's Feedback
Answer / aju
We can choose the cable according to the current rating
after considering overload and voltage drop factors
Usually cables are loaded upto 75-80 % of the rating
specified by manufacturer ..
For instance, if you need to choose a cable for a current
rating of 25 A, we can simply choose 6 sq.mm cable since it
can carry 35 Amps. It is desirable not to use 4 sq.mm cable
which has a current rating of 28 A since it has no
sufficient spare capacity for overload condition.
Again, the cable size also depends upon the voltage drop
which depends upon the length of the cable....
usually voltage drop must be within 3-5 % range.If it
exceeds this limit then next higher size must be used until
it satisfies the 3% range
Eg. for calculation of voltage drop in 25A, 240V single
phase feeder having 150M length
Voltage drop/Ampere/Metre for 35 Sq.mm cable=2.1mV
Voltage drop= (2.1x25x150)/1000 =7.88V
% Voltage drop= (7.88x100)/240 = 3028%
Since it exceeds the 3% range, take next cable size
Voltage drop of 50Sq.mm cable= (1.6x25x150)/1000 =6V
% Voltage drop =(6x100)/240 =2.5%
Hence, we can select 50Sq.mm cable
| Is This Answer Correct ? | 74 Yes | 15 No |
cable size can be selected like ,suppose if u have any
motor with u of 110kw and its full load current is 190 then
when it is in dol stater starting torque is high up to 2
times of that full load so we have to use 300sq mm.if it is
in star delta 240 sq mm is enough because in a star
starting current is low it means 70 to 60 percent of full
load .after that some time delay delta pick ups
| Is This Answer Correct ? | 40 Yes | 21 No |
what happens to a turbo alternator if it get trip and 1 out of 3 poles of circuit breaker in close condition
Dear sir, please tell me how many day use CTPT transformer
1 Answers Daya Engineering Works,
sigal phase supply is 230 v ac two phase supply is 415 v ac then why three phase supply having supply is 415 v ac why not 690v ac
I am designing new project sub station with 220 kV / 11 kV, 40 MVA capacity. This project have many recifier sets, which can generate 3rd harmonics. Now I have to select vector group of This transformer. To minimise 3rd harmonics, what care should I take in selection of Transformer Vecrtor group? If it is Y-Y with open Delta tertiary then what should be the rating & voltage of Tertiary Winding?
which transfofrmer oil break down voltage strength get will be more if oil sample taken from bottom of tank or oil sample taken from top of the transfomer tank.
what is stper motor.what is its uses
the electric traction poles having 3 cables n two cables touches with a insulator (or any) another one separated but it will be running 1-phase why?
How to calculate the transmission losses incase of overhead transmission lines?
why plc need seprate earthing?
why distribution transformer are of DY11 type?
how we can differentiate a motor and a generator just by a glance?
i need of the bhel question papers along with answers and also give some website names for the downloading question (electrical and electronics engg question)please help me....
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)