why plc need seprate earthing?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
All electronic equipments require a seperate earthing ,to
avert adverse effect of high voltage surges caused by earth
faults .
| Is This Answer Correct ? | 27 Yes | 1 No |
Answer / viral
I will like to add one more reason, in case the earthing
opens between panel and ground then the fault tend to
divert directly to PLC panel. This in return will blow off
cards in PLC. Thus the earthing is kept different.
| Is This Answer Correct ? | 5 Yes | 0 No |
What is the meaning of STAR POINT? Why this important in CT and VT?
We need to current density & short circuit calculation at 65kA for aluminium & copper busbar.
how the global warming take place?
Is it possible to measure correct value of earth resistance & cable insulation ristance with out disconncting earth lead & both sides of cable ends? If not, any other method to measure ER & CIR with out disconneting from the system.
What is the equivalent circuit of a transformer and its vector diagram?
How impulse levels are calculated that for 11kV impulse is 75kvp, for 24kV impulse is 125kvp ?
How to Calculate the maximum Demand required for a connected load for a manufacturing Plant
slor cell made?
which starter is used for synchronous motor
what is O.T?specify the acceptable range?
What do you mean by creepage distance?
i have 6oo kva dry type transformer and its neutral is not grounded even body of transformer ground i want to know it is safe or not ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)