why plc need seprate earthing?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
All electronic equipments require a seperate earthing ,to
avert adverse effect of high voltage surges caused by earth
faults .
Is This Answer Correct ? | 27 Yes | 1 No |
Answer / viral
I will like to add one more reason, in case the earthing
opens between panel and ground then the fault tend to
divert directly to PLC panel. This in return will blow off
cards in PLC. Thus the earthing is kept different.
Is This Answer Correct ? | 5 Yes | 0 No |
what is difference between fuse and circuit breaker?
What will happen to the speed of synchronous machine subjected beyond the pull out torque? Are the behavior shown by rotor remains same for both the alternator and motor?
IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoing breaker kA rating to be equal to busbar kA rating?
which capacity of RCCB used for five thousand watt electricity load?
How to Select a Transformer Rating ?
3 Answers Tata Steel Limited, Techno Electric and Engineering, Vedanta,
why we use the fuse in only one wire? althrough in ac current the current flows in both directions. why the neutral wire can be taken half the magnitude of phase wire while same current returns from neutral wire?
An active element is one which a. Supplies energy b. Absorbs energy c. Supplies energy and convert energy from one form to another
why we are using Load factor?
why C.T secondary are rated 5A generally?
In three phase supply why we use R Y B Colour not other.
I need to connect a synchronous generator to the grid using automatic synchronization and two circuit breakers (one for synchronization, one for end connection to the grid), how to determinate the required diameter of the cables?
We have 90mX100m hangar with 16 no.of supporting pillar. It is required to provide power supply on all pillars. what is suggested earthing scheme for hangars.