what happens to a turbo alternator if it get trip and 1 out
of 3 poles of circuit breaker in close condition
Unbalanced current will develope till the upstream end
circuit breaker protection detect ( inverse time overcurent
and earth fault)and trips and isolate the fault.
The turbo alternator can run till negative sequence
charactristic constant limitation.I2t=K. Only generator
winding overheat and some time sparks,de[pends on fault.
It is also observed that major accident took place not only
damaging generator circcuit breaker pole damages,arcs and
body cabinet,arc chute burned,turbo alternater bearing
failure nted.
Is This Answer Correct ? | 2 Yes | 0 No |
why to need a electrical earthing?
How shall i design a liquid rotor starter
Difference between field rheostat and armature rheostat.
why rating of alternator in kva & induction motor in kw
what is the difference between thermal magnetic release and microprocessor based release breakers. what are the advantages of latter over the first one...
5 Answers Jackson, Karthik Industries, McD BERL, TCS,
Is there any design in the world a 220 KV transformer without breather …??????
what is the meaning for va and how it is generated
What is rotating transformer? Which machine is used specifically as rotating transformer?
generally on the roadside v hav 11kv line which is being step down to 440v line to line....so any1 can tell me which type of transformer they r using whether it is star to delta,delta to star etc...???
Please provided formula for calculate the cable size from step up transformer to M.V panel, run overhead aluminum cables, total load is 5mega watt, total length 900 feet.
if any leas acid battery is having low or high sp.gravity taen what will be effect of battery and why
How to calculate cable sizing