Answer / samuel
Dyn11 distribution transformer, primary side Delta connection is with the reason of alleviating the effect of secondary winding's any of other than similar phase effect in the primary side. with the concept of magneto motive force. Secondary winding star with neutral is required for customers with requirement of single phase with ground........
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / naga
DyN11 distribution tr is used as neutral wire in secondary
is required and winding connections are easy and simple
| Is This Answer Correct ? | 2 Yes | 7 No |
Answer / k.prakashchandra
DyN11 distribution tr is used as neutral wire in secondary
is required and winding connections are easy and simple.
| Is This Answer Correct ? | 4 Yes | 10 No |
Answer / s.panneer selvam
In Dy11 secondary leads primary by 90 degree means in case of any fault the secondary protection which is sensitive than primary will always senses the fault before and enable to trip. the reason behind is to enable protection not to allow more current to flow through the circuit in the event of fault or abnormality. star point needed for neutral and we use have single phase load are of secondary reason and i think the primary reason may be this which i read from MG say book
| Is This Answer Correct ? | 1 Yes | 8 No |
Difference between On Line capacitor and Station Type capacitor.
what is leading and laging please in details
why auto transformer connected in star?
how to calculate the ngr capacity(nutral grounding resistor)
What is Automatic Voltage regulator(AVR)?
1kva=how many kw & amps
What is the types of HT motor testing
why we define potections of Tourbo generator in Class A & B.
we r having 3 core 3 1/2, 4 core cables how we can know this cable has to be used for this purpose?
How to design a Unit auxiliary transformer for a power house having a unit of 65 MW and Generating voltage of 11 KV and Secondary voltage of 433V
Can VFD step up to 60 Hz if it is designed to receive 50 Hz input?
what is the maximum temperature rating of a thhn insulated conductor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)