6 MVA transformer secondary is rated for 725V at no load.
The incommer ACB is rated at 690 V, 3200 Amp. Would there
be any effect on performance of ACB due to lower voltage
rating?
Answers were Sorted based on User's Feedback
Answer / mnm
Your selection is OK. Any breaker will have 110% voltage
withstand capability. Only thing is interruption capability
reduces, which is not relevent on no-load. On load, the
voltage of the transformer will reduce by nearly 6%, due to
impedance, making it just suitable.
| Is This Answer Correct ? | 1 Yes | 1 No |
ACB is not suitable as transfomer secondary voltage level
is higher than ACB voltage level which cause insulation
failure of the ACB and cause of flash.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / loke
We can agree with Mr.Mnm because actually the rating of
breaker ia 690v and it will be having with stand capacity of
+_10% so it can with stand upto 765v & also check out with
the impedence it would be around 6-9% from that also you can
check secondary voltage of t/f.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / joe
there wil be no effect because in transformer the input and
the output is difference due to the coil winding
| Is This Answer Correct ? | 1 Yes | 5 No |
In Swinburne's Test on D.C.machines, why the efficiency is more when the machine runs as generator than when it runs as motor???
6 Answers College School Exams Tests, GE, MVR, Practical Viva Questions,
whats the necessary to correct the power factor using capacitive banks in industries?
what is the excess air in furnace
what is the advantage of connecting capacitors in delta than in star?
How to increase home power factor? Can we connect capacitor directly? How to select capacity of capacitor?
what i the full form of ABS 111 in transformer.
In view of Electrical Engg. What is the use of SCR(Silicon control rectifier)
what is the formula for transformer oil?
Why silica gel use?
What is the rating of a circuit breaker needed for 300 kv load in 33KV supply line of 33/415 transformer ? Whether 800/1200 amp vaccum circuit breaker can perform for a 33 KV line in input in 415 volt in output of the transformer ?
In which reason, one end of CT secondry get connected with Earthed? Normaly S1 of CT. Why????
i am gng to visa interview this july i have 4 backlogs gre 1010,toefl 75,pls give me the tips pls pls
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)