Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


6 MVA transformer secondary is rated for 725V at no load.
The incommer ACB is rated at 690 V, 3200 Amp. Would there
be any effect on performance of ACB due to lower voltage
rating?

Answers were Sorted based on User's Feedback



6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / rvg

The transformer details shows no load voltage and we can
assume about 3-4% decrease with full load. ACB with rated
voltage 690 should not be suitable for 725V. ACB's nominal
voltage should be 1.414 time the applied voltage.

Is This Answer Correct ?    6 Yes 2 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / mnm

Your selection is OK. Any breaker will have 110% voltage
withstand capability. Only thing is interruption capability
reduces, which is not relevent on no-load. On load, the
voltage of the transformer will reduce by nearly 6%, due to
impedance, making it just suitable.

Is This Answer Correct ?    1 Yes 1 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / praveen kumar gupta

ACB is not suitable as transfomer secondary voltage level
is higher than ACB voltage level which cause insulation
failure of the ACB and cause of flash.

Is This Answer Correct ?    0 Yes 0 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / loke

We can agree with Mr.Mnm because actually the rating of
breaker ia 690v and it will be having with stand capacity of
+_10% so it can with stand upto 765v & also check out with
the impedence it would be around 6-9% from that also you can
check secondary voltage of t/f.

Is This Answer Correct ?    0 Yes 1 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / joe

there wil be no effect because in transformer the input and
the output is difference due to the coil winding

Is This Answer Correct ?    1 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

In Swinburne's Test on D.C.machines, why the efficiency is more when the machine runs as generator than when it runs as motor???

6 Answers   College School Exams Tests, GE, MVR, Practical Viva Questions,


whats the necessary to correct the power factor using capacitive banks in industries?

2 Answers  


what is the excess air in furnace

0 Answers  


what is the advantage of connecting capacitors in delta than in star?

1 Answers   NTPC,


How to increase home power factor? Can we connect capacitor directly? How to select capacity of capacitor?

5 Answers  


what i the full form of ABS 111 in transformer.

1 Answers   Birla, Ford,


In view of Electrical Engg. What is the use of SCR(Silicon control rectifier)

11 Answers  


what is the formula for transformer oil?

1 Answers  


Why silica gel use?

1 Answers   PWD,


What is the rating of a circuit breaker needed for 300 kv load in 33KV supply line of 33/415 transformer ? Whether 800/1200 amp vaccum circuit breaker can perform for a 33 KV line in input in 415 volt in output of the transformer ?

0 Answers   Hira Group,


In which reason, one end of CT secondry get connected with Earthed? Normaly S1 of CT. Why????

1 Answers  


i am gng to visa interview this july i have 4 backlogs gre 1010,toefl 75,pls give me the tips pls pls

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)