6 MVA transformer secondary is rated for 725V at no load.
The incommer ACB is rated at 690 V, 3200 Amp. Would there
be any effect on performance of ACB due to lower voltage
rating?
Answers were Sorted based on User's Feedback
Answer / mnm
Your selection is OK. Any breaker will have 110% voltage
withstand capability. Only thing is interruption capability
reduces, which is not relevent on no-load. On load, the
voltage of the transformer will reduce by nearly 6%, due to
impedance, making it just suitable.
Is This Answer Correct ? | 1 Yes | 1 No |
ACB is not suitable as transfomer secondary voltage level
is higher than ACB voltage level which cause insulation
failure of the ACB and cause of flash.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / loke
We can agree with Mr.Mnm because actually the rating of
breaker ia 690v and it will be having with stand capacity of
+_10% so it can with stand upto 765v & also check out with
the impedence it would be around 6-9% from that also you can
check secondary voltage of t/f.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / joe
there wil be no effect because in transformer the input and
the output is difference due to the coil winding
Is This Answer Correct ? | 1 Yes | 5 No |
what is the use of buchzloys relay?
What are the advantages of speed control using thyrister?
The power showed in the name plate of the motor is input power or output power?? The power showed in the name plate is 18.5kw measured current is 34.5 amps. location is india. can i calculate the efficiency of the motor using this data??
What is the Ramping rate of Generator. What mena Ramping rate
why we use circuit breakers for switching instead of normal switching device?
How can we select a capacitor Bank.? i need a standard formula for that.?
3 Answers ABB, Ace Info, HAL, IKK, MahaGenco,
what would happen nif we increase or decrease the capacitor of a flood light.
In control room of our one plant there is a continuously the incoming power goes to PC is vary,means in stabilizer it continuously indicate from high input to low and low input to high. what is the reason and its solution.
i need list of swg(standard wire guage) or area of conductor v/s current carrying capacity of conductor copper & alluminium...
what is the relationship between phase & neutral
what will happen if dc motor given ac supply
what is the formula for calculation of sac?