Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


6 MVA transformer secondary is rated for 725V at no load.
The incommer ACB is rated at 690 V, 3200 Amp. Would there
be any effect on performance of ACB due to lower voltage
rating?

Answers were Sorted based on User's Feedback



6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / rvg

The transformer details shows no load voltage and we can
assume about 3-4% decrease with full load. ACB with rated
voltage 690 should not be suitable for 725V. ACB's nominal
voltage should be 1.414 time the applied voltage.

Is This Answer Correct ?    6 Yes 2 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / mnm

Your selection is OK. Any breaker will have 110% voltage
withstand capability. Only thing is interruption capability
reduces, which is not relevent on no-load. On load, the
voltage of the transformer will reduce by nearly 6%, due to
impedance, making it just suitable.

Is This Answer Correct ?    1 Yes 1 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / praveen kumar gupta

ACB is not suitable as transfomer secondary voltage level
is higher than ACB voltage level which cause insulation
failure of the ACB and cause of flash.

Is This Answer Correct ?    0 Yes 0 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / loke

We can agree with Mr.Mnm because actually the rating of
breaker ia 690v and it will be having with stand capacity of
+_10% so it can with stand upto 765v & also check out with
the impedence it would be around 6-9% from that also you can
check secondary voltage of t/f.

Is This Answer Correct ?    0 Yes 1 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / joe

there wil be no effect because in transformer the input and
the output is difference due to the coil winding

Is This Answer Correct ?    1 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

1. transformer design formula ? 2. how to calculate the primary turns and secondry turns ? 3. core types ? 4. how to find the primary current and secondry current ? 5. how to calculate the stacking factor ? 6. range of fulx density ?

2 Answers   Automation, Indian Railways, Mogora Cosmic,


what is transient enclosure vltage , very fast transients, very fast transient over voltages

0 Answers  


what is different between installation and commonissonig.

3 Answers  


1. what is the power factor and whatis his losses 2. what is the working procedure of 51RNB AND 87 relay

3 Answers   ABB,


What is the make of breakers, transformers, generators? What are their capacities and ratings?

1 Answers  


how electricity is generated through electeic generator ?

1 Answers  


Why the underground cables will Punchar? or what is the reason to burst the underground cables?

1 Answers  


6. A DC AMMETER HAS R=0.1 OHM & CURRENT RANGE IS 0-100 A IF THE RANGE IS TO BE EXTENDED TO 0-500 A THEN METER REQUIRES SHUNT RESISTANCE OF ..........

2 Answers   SSC,


Whats the difference between three phase and single phase?

4 Answers  


Earth bits close or open. Which is correct

0 Answers  


I HAVE A INCOMING 100A MCCB TPN 25KA, CABLE LENGHT OF 80M 70MM CABLE SIZE FROM MAIN SUBBOARD TO NEW DB.BASE ON THE FAULT LEVEL SETTING OF 45KA.I WOULD LIKE TO FIND OUT 25KA ENOUGH KA. APPRECIATE IF SOMEBODY CAN ASSIST ME WITH FORMULA FOR THIS. FRM: JEFF

0 Answers  


Which Motor used in Fan's Motor ?

3 Answers   Matsui Technologies,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)