6 MVA transformer secondary is rated for 725V at no load.
The incommer ACB is rated at 690 V, 3200 Amp. Would there
be any effect on performance of ACB due to lower voltage
rating?
Answers were Sorted based on User's Feedback
Answer / mnm
Your selection is OK. Any breaker will have 110% voltage
withstand capability. Only thing is interruption capability
reduces, which is not relevent on no-load. On load, the
voltage of the transformer will reduce by nearly 6%, due to
impedance, making it just suitable.
Is This Answer Correct ? | 1 Yes | 1 No |
ACB is not suitable as transfomer secondary voltage level
is higher than ACB voltage level which cause insulation
failure of the ACB and cause of flash.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / loke
We can agree with Mr.Mnm because actually the rating of
breaker ia 690v and it will be having with stand capacity of
+_10% so it can with stand upto 765v & also check out with
the impedence it would be around 6-9% from that also you can
check secondary voltage of t/f.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / joe
there wil be no effect because in transformer the input and
the output is difference due to the coil winding
Is This Answer Correct ? | 1 Yes | 5 No |
If Polarization index of motor 8.75 at 500volts of medium voltage 4.16 KV motor what this mean winding good or bad pl answer if any reffrence book give me the link
as per standards how many neutral earthings and body earthings are needed.please help me
what is meant by line voltage and phase voltage in a three phase transformer?
meter ratio is 100/5 CT ratio is 125/5, when the ratios changes i.e., CT ratio is 125/5 meter ratio is 100/5 what is the MF in boths conditions?
What is meant by transformer, why it should be used, with out that equipment what happens if we transformed the supply?
how a generating station can monitor its multi users power factor. What type of incentive /penalty is associated with power factor management.
Why we choose 400kv,220kv,132kv,66kv,33kv transmission voltages for transmitting power. Why not other voltage levels.
21 Answers College School Exams Tests, HC, HCL, Jaypee, JPMorgan Chase,
How does a diesel generator works?
what is rated voltage?
My system is 22kv/3.3kv transformer. client is asking to use NGR, but as we have dedicated Neutral Earthing systems which has a value less than 1 Ohm. So i want solid comparision. Why i should not use NGR as my system is already protected.Can any one help me to get out of this.how should i reply on basis of some great comparision and calculations. Please help
Why we are not placing c.B 's btwn generator and transformer.? what happens when generator gets disconnected from transformer when it is running @ full load?
why rating in KVA and KVAR?