Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


6 MVA transformer secondary is rated for 725V at no load.
The incommer ACB is rated at 690 V, 3200 Amp. Would there
be any effect on performance of ACB due to lower voltage
rating?

Answers were Sorted based on User's Feedback



6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / rvg

The transformer details shows no load voltage and we can
assume about 3-4% decrease with full load. ACB with rated
voltage 690 should not be suitable for 725V. ACB's nominal
voltage should be 1.414 time the applied voltage.

Is This Answer Correct ?    6 Yes 2 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / mnm

Your selection is OK. Any breaker will have 110% voltage
withstand capability. Only thing is interruption capability
reduces, which is not relevent on no-load. On load, the
voltage of the transformer will reduce by nearly 6%, due to
impedance, making it just suitable.

Is This Answer Correct ?    1 Yes 1 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / praveen kumar gupta

ACB is not suitable as transfomer secondary voltage level
is higher than ACB voltage level which cause insulation
failure of the ACB and cause of flash.

Is This Answer Correct ?    0 Yes 0 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / loke

We can agree with Mr.Mnm because actually the rating of
breaker ia 690v and it will be having with stand capacity of
+_10% so it can with stand upto 765v & also check out with
the impedence it would be around 6-9% from that also you can
check secondary voltage of t/f.

Is This Answer Correct ?    0 Yes 1 No

6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200..

Answer / joe

there wil be no effect because in transformer the input and
the output is difference due to the coil winding

Is This Answer Correct ?    1 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

Whet is IGBT.How it teste

2 Answers  


please tell 1 ton equal to how many kilo watt?? in some converter software's that is 3.5 kw. is it right?

8 Answers   Mitsubishi,


What is the test block protection relay if any body know plz explained

0 Answers  


why we provided electrical earthing?

5 Answers   CPCL,


How will you justify IR value and Charging voltage of any motor,transformer and Cables.......???? . . . . . . . . Plz tell me any body Baljeet Singh, engineer_89@refiff.com

0 Answers  


why power factor occur only inductive load not in resistive ?

8 Answers  


16kv transformeris stolen in my village.and department is not taking action.then what should i do.any shortcut .please help any idea

1 Answers  


What is the life of MCCB

1 Answers   Siemens,


why corona ring is used in out door switchyard lightning arrestor

3 Answers  


what is megar healthy value for ht &lt cables

2 Answers  


what is voltage ?

7 Answers  


How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test?

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)