What happens when the polarity changes in CT? Explain
briefly?
Answers were Sorted based on User's Feedback
Answer / m s venkateswara rao
polarity of the CT secondary is depend up on the polarity of CT primary. For example current flow in primary of a CT is considered from P1 to P2 current flow in secondary will be from S1 to S2. If the CT is used for multi function meter to measure the Active power, apparent power will show negative readings if polarity is changed. If is used for protection and the type of protection is considered is non directional over current/ earth fault there is no difference in CT polarity change. If it is directional over current/earth fault relay will not operate because it will never seance positive value as the protection type is directional.So by changing the polarity of CT, protection for which we opted will defeated.
| Is This Answer Correct ? | 32 Yes | 1 No |
Answer / digvijay
My question regarding worng connection in any phase of ct,
Is there any effect on power factor of that phase which is wrongly connected
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / sanjiv c keshari
CT means current transformer are used for earth fault protection and current showing.If polaraty has changed so CT will not work proper it is showing wrong reading.
| Is This Answer Correct ? | 4 Yes | 9 No |
Answer / monojit dutta
IF POLARITY CHANGES, THE DIRECTION OF THE CURRENT FLOW WILL
ALSO CHANGE.
| Is This Answer Correct ? | 4 Yes | 9 No |
Answer / guna
CT - current transformer, other name is instrument transformers, which are used to measure high currents. By depending upon winding ratio (Ex,20:5) it gives the current value at the user end. if we change the polarity means (5:20) either it will show high current nor it can get short circuited due to abnormal current flow on the LT side.
| Is This Answer Correct ? | 2 Yes | 15 No |
consider the example of CT with the ratio 50:5.
it means if 50amps is flowing in the primary,it will show
only 5 amps in the secondary.Now when the polarity is
changed,50 amps will flow in the secondary which is
comparatively high,and the windings are designed to carry
only 5 amps and hence as a result the windings will burn due
to the volumenous amount of current flowing throught he circuit.
| Is This Answer Correct ? | 4 Yes | 41 No |
Where r use in Dc motor in power plant?
what is the tolerance of electrical frequency for India? it's .5% or 1%?
how capacitor active and reactive.
1)which height building required lightning arrester? 2)how to calculate the requirement of lightning arrester? 3)what is the pro instrument? 5)how to test protective relay like overload?earth fault relay?
11KV electrical line going through the forest in cloudy night ,how can we find the direction of line.
5 Answers Bhel, Cesco, HZL, Nesco,
i want to trigger ATS (Mains +Generator )from external system could any body help me in this regard ?? is it posible if yes please tell me how?
it says in neutral wire current flows under normal condition, but when we put tester it wont glow, why?
What is an 86-P or an 86-A trip
For the same power rating,which motor is bigger in size,AC or DC?
what is corona
Suppose i Have an Ac motor of 25Hp 1500 Rpm 50 Hz Can i run a motor 2500 Rpm by AC drives by increasing a frequency either it safe or not ....
Why Power generation in India is at 50Hz while in America its 60Hz so is there any advantage/Disadvantage of this ??
38 Answers Australia Visa, College School Exams Tests, Fiat, InfoPlus, L&T, NTPC, TCS,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)