what is the current rating of 2500 KVA,33KV/433v transformer
on secondary(LT) side
Answers were Sorted based on User's Feedback
Answer / srinivasa rao talasila
Primary current=2500000/1.732*33000
=43.74A
Secondary current is =2500000/1.732*433
=3333A
| Is This Answer Correct ? | 43 Yes | 4 No |
Answer / pillay
sec 433volts of a 3 phase 2500 KVA TXformer will be
2500,000 / 1.72 / 433 = 3356 amps.
| Is This Answer Correct ? | 13 Yes | 5 No |
Answer / raj
input power= output power => transformer do's.
depends on ur load they will design.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / gopal
HT CURRENT
I=LOAD/VOLTAGE
I=2500X1000/33*1000=75.75A
LT CURRENT
I=LOAD/1.732*433
I=2500*1000/1.732*433=3333A
OR USE SIMPLE FORMULA
1=LOAD X 1.4
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / l rc reddy
ht capacitors starting time line current load&unload
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / gnanendra
Hey.. It is very important to mention whether it is 1-phase or 3-phase.. See any text book.. If rating given means in that it will be definitely mentioned..
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / s bharath
p=1.732*v*i*0.8
2500=1.732*433*i*0.8
i=2500*1000/1.732*433*0.8
i=4.16kA
| Is This Answer Correct ? | 6 Yes | 8 No |
Answer / kaami
power in = power out
v*i = v*i=2500kVA
on input side
33kv*i=2500kv
i=2500/33=75.75amps
on output side
v*i=2500kva
433v*i=2500Kva
i=2500/433=5.7ka
so it is designed for 5.7KA on secondary side
| Is This Answer Correct ? | 19 Yes | 22 No |
Answer / rafeek
p=3^1/3*vicos$
=3^1/3*415*i*0.8
p = 575i
p=250*0.8=200kw
200*1000=575i
i=347.82
i=347.82*1.2=417.39
i-~=400amps
| Is This Answer Correct ? | 3 Yes | 9 No |
neutral earth resistance testing is it possible for transformer while in load condition
what is the difference withbeen lighting capacitor and motor capacitor?
how we can select MCB ratings according to Voltages, Curves.
In LT Line What is the minimum clearance required between phase to phase busbar & between Phase to body of the panel? Also between Neutral &phase, & Neutral & body of panel. as per standards.
How many loops can be provided in a circuit as per IS rules.?
what are the types used for alternator earthing,what will happen if more than two alternator is working in parallel with each having own system earthing.is there any possibility for circulating current in between two system.
what happens if DC earthing and AC earthings are shorted?
Can earth resistance be measured without connecting the earth electrode? and should earthing connections be disconnected What is the effect of connecting two cables of different sizes in parallel with supply? Thanks in Advance. I am intrested to get in touch with some tecnocrats/engineers,my mail i.d is : hiremathvijay@rediffmail.com
how to check 3phase motor winding with help of multimeter?
How can we measure MVAR of a 3 phase transformer.....???
what is the difference between electrical degree n mechanical degree?
How can we find out earth leakage,(shock)in side the house?.. (with out ELCB)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)