what is the current rating of 2500 KVA,33KV/433v transformer
on secondary(LT) side
Answers were Sorted based on User's Feedback
Answer / srinivasa rao talasila
Primary current=2500000/1.732*33000
=43.74A
Secondary current is =2500000/1.732*433
=3333A
| Is This Answer Correct ? | 43 Yes | 4 No |
Answer / pillay
sec 433volts of a 3 phase 2500 KVA TXformer will be
2500,000 / 1.72 / 433 = 3356 amps.
| Is This Answer Correct ? | 13 Yes | 5 No |
Answer / raj
input power= output power => transformer do's.
depends on ur load they will design.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / gopal
HT CURRENT
I=LOAD/VOLTAGE
I=2500X1000/33*1000=75.75A
LT CURRENT
I=LOAD/1.732*433
I=2500*1000/1.732*433=3333A
OR USE SIMPLE FORMULA
1=LOAD X 1.4
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / l rc reddy
ht capacitors starting time line current load&unload
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / gnanendra
Hey.. It is very important to mention whether it is 1-phase or 3-phase.. See any text book.. If rating given means in that it will be definitely mentioned..
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / s bharath
p=1.732*v*i*0.8
2500=1.732*433*i*0.8
i=2500*1000/1.732*433*0.8
i=4.16kA
| Is This Answer Correct ? | 6 Yes | 8 No |
Answer / kaami
power in = power out
v*i = v*i=2500kVA
on input side
33kv*i=2500kv
i=2500/33=75.75amps
on output side
v*i=2500kva
433v*i=2500Kva
i=2500/433=5.7ka
so it is designed for 5.7KA on secondary side
| Is This Answer Correct ? | 19 Yes | 22 No |
Answer / rafeek
p=3^1/3*vicos$
=3^1/3*415*i*0.8
p = 575i
p=250*0.8=200kw
200*1000=575i
i=347.82
i=347.82*1.2=417.39
i-~=400amps
| Is This Answer Correct ? | 3 Yes | 9 No |
what is the operation of UPS ? can any one answer me?
What is Gnat,Ant,Rabbit &Dog overhead conductor? Please explain.
on 22.03.2015 at 17:15hrs Y phase 66kV class Power Trf-2 Current transformer has flashed over and oil came out. The failed CT has been replaced on 24.03.2015 at 13:15hrs and the Trf has been charged in presence of RT Hassan after conducting the pre-commissioning tests. On the same day at 17:00hrs the commissioned CT has again flashed over and immediately the Trf has been isolated from power supply. It is confirmed the secondary is not opened and checked the earth integrity and is found ok. Here what would be the reason for the CT failure?
what is the function of CRGO in a Transformer?
hi frds, i m electrical engineer.can i get cdr for electrical engineer if u have then send me on my mail id its jayesh_ee88@yahoo.com.please help me frds
how can we change the phase angle b/w two phase?
how to calculate the current carring capacity of the conductor
Why nutral wir used thinner than phase wire
What are the safety devices on Cumins Diesel Generators from 500 kva to 1500 kva.
how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec.
power is the product of voltage and current.so we can measure the value of power just by using ammeter and voltmeter.......then why do we use a wattmeter?
What is difference between mcb and mccb.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)