what is advantage in open delta connection?
Answers were Sorted based on User's Feedback
Answer / prr
an open delta can continue to supply power,when one of the
transformer, out of 3,is disabled or removed for
maintenance ,even thiugh with reduced capacity ie 57 %.
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / dwi tjahjono
Open delta connection (for PT as protection) usefull to detect the shifting voltage during normal and faulty condition.
We can use this to set the directional relay
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / prasad@clp
Open delta used in inter turn fault protection of generator
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rman
its very cheap because you only need 2 transformers. but the total capacity of these 2 transformers cannot be used remembering that the rating of each transformer is multiplied by a factor of sqrt(3) which is only 1.73
i.e. two transformers rated at 50kVA to be open delta.
the total is 2(50kVA) which is 100kVA but the transformer can only carry 1.73(50kVA) which is only a total of 86.5kVA
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / t.govind
this open delta using protection for generator stator earth fault .
95 % stage ths cald residual voltage
third core of the PT secondary is connected delta connection when the fault accur in the stator voltage will came fr exmple 5o v . normaly it was 0 volt
exm : PT secn 3a 3n 3a 3n 3a 3n ..
frst 3a and last 3n fr out put vltg measrn at this poit only
other connection fst 3n to secnd 3a .second 3n to thrd 3a . & 3rd 3n .
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / manoj
for ungrounded system only we are using open delta for
finding earth fault.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ahmed abdel fattah
هذه المشاركة ذات صلة بملتقى المهندسين العرب :
http://www.arab-eng.org/vb/t205463.html#ixzz1b3W23GT1
The open delta transformer connection can be made with only
two transformers instead of three (figure below). This
connection is often used when the amount of three phase
power needed is not excessive, such as a small business. It
should be noted that the output power of an open delta
connection is only 87% of the rated power of the two
transformers. For example, assume two transformers, each
having a capacity of 25 kVA, are connected in an open delta
connection. The total output power of this connection is
43.5 kVA (50 kVA x 0.87 = 43.5 kVA).
Figure : Open Delta Connection
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / shajina
Advantages of open delta are :
• power supply can be continued in balanced condition but with lesser rating ie, derated operation.
• very useful in mining industry where continuing is needed.
•maintenance and repair work can be done on one of the transformer while power is supplied to the consumers.
•cost is less for open delta connection.
•flexibility of power supply at 2 different levels.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is allowable current flows from phase to ground with out tripping the breaker
In LT cables 3.5 core cable are available that means 3 core and .5 for neutral Why .5 for neutral and is there any reason for that please suggest thanks and regards pavan kumar
what will happen, if both relay contact has live supply, and coil of relay activated
what is mean by live tank and dead tank in current transformers?
what is auxilliary transformer??
how to check the earth resistance value& what is the minimum earth resistance for good earthing sysytem.
33 Answers Brookfield, BSNL, DMRC, Epoch, KPTCL, Polycab, Power Control, SIEA, Siemens, Wipro,
What is A.C Resistance for Earthing ?
why do we put a transformer on soak before loading it
dear sir/madam i want to get some knowledge about RRB EXAMINATION(section engineer) 1- what is minimum cut off 2- wht portion is major portion . 3- can any body provide Sample paper. thanks & regards ashish
why the armature coil in dc machine is round?? swagat k.
What is the disadvantage in proportional controller?
generator(Deutz 550kv)is runing for 2 hours with load of 900 amp and then it goes in shutdown with alarm fault messege of speed fault although heirtz reading fixed at 50,what does that mean
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)