In LT cables 3.5 core cable are available that means 3 core and .5 for neutral Why .5 for neutral and is there any reason for that please suggest
thanks and regards pavan kumar
Answer / amarjit singh
becase in neutral always unbalanced current flow in 3 phase system if current in amp R=25 A,Y=22 A AND B=20A only 5 amp current flow through neutral thats why in 4 core cable neutral diameter less than phases .try it practically
| Is This Answer Correct ? | 0 Yes | 0 No |
I hv a question regarding power factor improvement just after transformer. I request you to reply me plzz. thank you sir. My friend has a small unit of fabrication. in his factory the main load is a welding machine, lathe machine, grinding machine. this load is not continuous type. now our electricity board has installed 16 KVA, 11000/433 V transformer for our factory. In the energy meter (trivector meter) at LV side of transformer, i hv seen power factor value of 0.15 only when only 3 KW load was flowing. Further electricity board has suggested to install 4 KVAR capacitor at LV side after energy meter. Now my question is that if we permanantly install and switch on 4 KVAR capacitor after energy meter, during some load on transformer and also without any load on transformer, wht will be the power factor shown in energy meter?i dont want to get any penalty by electricity board, so plz suggest me if i can permanantly install and switch on the 4 kvar capacitor or not at LV side of transformer just after energy meter? Thank you again and awaiting for ur positive reply soon.
circuit breaker is ...............connected with circuit
Diagram on interconnectivity of 11kv transformer with RMU (i.e, one incoming and two outgoing or two incoming and one outgoing)
why do we have spikes enough to burn electronic boards, when generators are not grounded
can we install HT panel & LT panel side by side or how much clearance is required ?
How can we define 'Phase'
What do you mean by a phase angel of instrument transformer?
Hi everyone, I'm Lachuu, recently joined automation company as PLC Engineer. I have certain basic question, I request all big gurus and seniors to answer these question. Because this will be very helpful to me as well starters like me. How to design a control circuit (ex: pick & place - my current project) Yamaha robot PxYx series controller RCX222, using 6 cylinder double acting, plc keyence kv p16r 2 expansion unit for input and output each. How to select panel terminal mcb elcb powersupply. My main concern in some projects how to select dc power supply, mcb rcb(I came across dif bt b c d curves, but stil confusing, pls help me :-(. I would really appreciate all who are going respond to this question.
can i know how to design overcurrent setting and earth fault for 11kv & o.433kv system assuming tx 1000kva.
why usa use 60hz and 110v?
what is formula in determining the size of Circuit Breaker for transformer with the following specifications. 7 units of 1600 volts (primary) and 400 volts (secondary). Both Primary and Secondary will have a circuit breaker which is SF6. What should be the Switchgear Main Breaker Size anf the sizes of each brances Circuit Breaker for Primary.
from generating station If 400v LT line length is 1000m how much voltage is drop and how do i calculate it? which cable will be use for this line?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)