how to check the earth resistance value& what is the
minimum earth resistance for good earthing sysytem.
Answers were Sorted based on User's Feedback
Answer / jaydeep parmar
value of the earth pit should be less then 2 ohm and earth grid value should be <1 ohm
| Is This Answer Correct ? | 428 Yes | 59 No |
Answer / tauseef tarique, engineer(e)
The earth resistance value can be checked by the use of
earth resistance tester (called megger earth tester). The
best earth resistance should be less than one ohm but the
permissible value is less than 5 ohm. For rocky areas it
should be less than 8 ohms.
| Is This Answer Correct ? | 318 Yes | 43 No |
Answer / pandiyarajan
Grid resistance value should be lessthan 1 ohm
| Is This Answer Correct ? | 209 Yes | 31 No |
Answer / aruna devi
By using earth megger .It should be less than 2ohm.
| Is This Answer Correct ? | 227 Yes | 72 No |
Answer / bhavini
earth tester use for measuring resistance of earth pit
should be less than 1 ohm.
| Is This Answer Correct ? | 105 Yes | 26 No |
As such there is no any standard of earth resistance value,
Its varies on different type of soil resistivity. Idley it
should be 0, but in different kinds of soil for electrical
equipment it should be better to below 10 Ohms and for
electronic equipment it should be better to below 5 ohms.
| Is This Answer Correct ? | 100 Yes | 28 No |
Answer / ramaraj.g
The earth resistance value can be checked by the use of
earth resistance tester (called megger earth tester). The
best earth resistance should be less than one ohm but the
permissible value is less than 5 ohm. For rocky areas it
should be less than 5 ohms.
we using the DMM in check the L - N , N- E ,E- L
this small calc
L-N - 230 v
N-E - BELLOW THE 2 VOLTS IS GOOD ERATH CONN
E-L - 230v IS RECONFORM TO GOOD EARTH OR NOT
L-N = E-L
| Is This Answer Correct ? | 77 Yes | 11 No |
Answer / bk sharma
It should be near <0.5 ohm for good earthing.
| Is This Answer Correct ? | 64 Yes | 11 No |
Answer / bhanu
earth testers are used. and it is checked wheathe earh
resistance range is from 1-2 ohm or not.
| Is This Answer Correct ? | 83 Yes | 39 No |
IF I USED VVVF DRIVE IN FAN APPLICATION MOTOR IN 6.6 KV ( 700 KW) MOTOR & DURING NORMAL RUN OPERATION TIME IF RPM SUDDENLY REDUCE IN MOTOR BY DRIVE(E. MOTOR RPM REDUCE SUDENLY 687 TO 550 RPM) WAHT WILL BE HAPPEND IN DRIVE
plz send me the procedure and syllabus for mseb exam
What is the minimum IR value of HT/ LT cable? Pls post separetely!!!!!
What is meant by Im=30mA@Vk/2. How to know the kee point voltage for CT design
how terminal voltage increases when load is capacitive (leading pf load)? (explain practically what is happening, not using phasor diagram
What is voltage
Dear all, Can anybody tell me that how to choose CT for a specific load? I have a 200kw induction motor, which ratio CT should be installed? Is there a formula or calculation that determines the CT ratio for a load? Regards.
what is the use of Auto re-closer?
what is the signification of trivector meter? why its name is trivector meter ?
Why the electron flow in reverse of current.
What do you mean by Stimulastion Test in Diesel Genarator / Why & when it's conducted ?
explain the meaning of harmonic resonance
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)