generator(Deutz 550kv)is runing for 2 hours with load of
900 amp and then it goes in shutdown with alarm fault
messege of speed fault although heirtz reading fixed at
50,what does that mean
Answer / k.prakashchandra
Gen voltage can not be 550 KV which I think ,is the tr
voltage. Hz is at 50 even after gen has tripped.That
means ,it was connected to grid.The gen might have tripped
on over speed due to load throw-off. If not, speed sensor
of the gen is to be checked
Is This Answer Correct ? | 0 Yes | 0 No |
why white color LED light is not possible?
1 “earthing” for bonding of equipment and circuits to common plant earth electrode potential, 2 “protective earthing (PE)” when this bonding is required for personal safety provisions 3 “grounding” for interference suppressing bonding of screens, sys-tems with ground level 4. low-impedance earthing ? 5.primary earthing system and secondary earthing system what is that? 6.earthing electrode or mesh net earthing electrode ? very confusing , simple but very informative help required ? i will be very very thankful to you guys.
what is difference between start imitation and start interlock for 3 phase motor protection ?
Why water bubbles when D.C. Current is passed through it? Why not when A.C. Current is passed?
why transformer ratings in kva?
99 Answers Bhel, College School Exams Tests, DOW, Emco, Esab, GE, KCP, PGCVL, Sodexo, TCS, vtps, Wipro,
how to prepare PPM schudule
HOW TO SIZE THE TRANSFORMER OR WHAT ARE THE STEPS INVOLVED IN FINDING THE SIZE OF THE TRANSFORMER FOR GIVEN LOAD SAY 2000KW ?
tell me about vfd
Can I use less voltage cable for neutral, since the voltage of return path is zero ideally?
Hi frnds :) plz tell me that i have 100 KVA 3 phase generator so by thumb rule 100*1.4 = 144 amps and generaly we can operate at 80% load...so it will 144*0.8 =112 amps.... so now i m confused about single phase load.....if we use that generator only for single phase the that 112 amps is total single phase load or i can give 112 amps at red 112 amps at yellow and 112 amps at blue.... i mean that total single phase load that 100 KVA generator will take is 112+112+112=336 amp ??
WHAT IS MEANING OF Gg & Gg IN hrc FUSE
Hydro P.P. run @ 600 rpm,8pole, Nucler P.P @ 1500rpm 4 pole , ThermlP.P @ 3000 rpm 2 pole.Why this diffrence??? when we can generate electricity @ 600 rpm then Why we had incresed speed in NPP & TPP???