generator(Deutz 550kv)is runing for 2 hours with load of
900 amp and then it goes in shutdown with alarm fault
messege of speed fault although heirtz reading fixed at
50,what does that mean
Answer / k.prakashchandra
Gen voltage can not be 550 KV which I think ,is the tr
voltage. Hz is at 50 even after gen has tripped.That
means ,it was connected to grid.The gen might have tripped
on over speed due to load throw-off. If not, speed sensor
of the gen is to be checked
| Is This Answer Correct ? | 0 Yes | 0 No |
why t/f are rated in kva. is it conserned with p.f.
12.5 KVAR capacitor 440V gas filled, Its used for windmill purpose, How can i know about microfarad value for this capacitor
WHAT IS THE SPECIFICATIONS CONSIDERED DURING DESIGN FOR THE OVER CURRENT RELAY?
What is the dc grounding system and what is diff between AC/DC grounding system?
in 11kv/400v transformer when only one phase of 11kv supply fails what happens to sec voltage and why
Diff between power trans and generating transformer?
Why Auto Transformer is called "Auto"? What is the logic?
why the Current transformers secodary is shorted to ground (In metering and Protection)
Define what is difference between fuse and breaker?
What is the fusing factor ?
4 Answers MESCOM Mangalore Electricity Supply Company Limited,
what is the relationship between induction motor and transformers?
11 Answers College School Exams Tests, Engineering, Reliance,
why we used to transmitt the power at higher voltage why not at lower voltage
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)