what is auxilliary transformer??
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Aux tr is located inside the station premises for the
supply at LT for station's own use only.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / k.prakashchandra
Transformer at a station for self-use.It is normally of
11KV/415V ratio
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / kingshuk dey
Auxiliary transformer is any transformer used for a separate dedicated part of the circuit/electrical system and does not supply to other parts.
For example, if you have a Motor Control Center with 5 buckets for 5 motors circuits, you can have one dedicated transformer for each of those circuits for control power. Each transformer will hence be an "auxiliary transformer".
Or you can have one transformer providing control supply to all circuits. That will be your "primary or main control transformer".
The prime reason for using auxiliary transformers is to isolate supplies for each equipment, such that if one is affected/damaged, the others are protected and are up and running. Or sometimes because that particular part of the circuit requires a separate supply. (Like, all other circuits can be controlled by 230 VAC, but one part requires 110 VAC, or you need to give dedicated 110VAC supply to SMPS for 24 VDC to PLC).
| Is This Answer Correct ? | 0 Yes | 0 No |
What are merits & De-merits of State-Space Method? What is series programming, parallel programming, general programming & direct programming ? And, difference between these programmings Techniques ?
How to obtain B license from TNEB license board. What is eligibility?
why the transformer is not operates on two phase?
1 Answers APGenco, Atkins, FFBL,
where to use CT and PT?
In our plant we are having 6.6 v motor wih MV drive running frm last two years.udenly at some speed motor getting vey vibrations what is the problem
Suppose i Have an Ac motor of 25Hp 1500 Rpm 50 Hz Can i run a motor 2500 Rpm by AC drives by increasing a frequency either it safe or not ....
Determine a suitable number of slors and conductors per slot for the starter 1 winding of a 3 phase, 3300 V. SO Hz 300 rpm alternator. The diameter is 2.3 m
How to calculate the heat load for a electrical room
why not feeling shock while touching rotor shaft of induction motor during running condition? during running condition emf induced in rotor.
directional relay is typically used to respond in fault condition who it can be used just as reverse power protection which purely senes direction reversal to operate a circuit breaker?
Why we use d.c. meger in a.c. induction motor?
how to find out this one mcb r mccb?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)