what are the difference between protection class CT and
Class PS CT
Answer Posted / selvam.s
Protection CT:
this type of CT can be used for protect the breakers.
5P10,5P15 & 5P20 are called protection current transformer
1) 5 means accuracy of sensing fault current
2) 'P ' means "protection"
3) 10,15 & 20 means ( no.of times ( 10,15 &20 ) X actual
current rating of breakers .
PS CT:
PS means protection special current transformer.
this type CT can be used for differential protection in
transformer & in alternator.
| Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
What happens to a motor if it is connected in Delta connection
what is different between phase and netural
How can you calculate the size of the down conductor cable for the lightning protection system. Is 70mm2 cable can replace 95mm 2 bare copper cable when the copper tape size is 25Wx3 thk mm.
why +24 v and -48 v give to BTS? If -48v protect from surge then why we not use -24 v?
Generation of voltage for each phase are same of a turbogenerator.Although the short circuit current flow when two phase of turbogenerator are shorted(where current can't flow without potential difference),why?
how hydrogen cooled alternator undergo maintanence ? that is hydrogen when come in contact with air can result into explosions .
how we calculate the withstansing current capacity of wires&cables?
What technology is used in latest generators?
What is resolution of a measurement?
WHat is the general checks required for Dry type transformers
What is online and offline ups? how does it works?
Do Phase angle measurement have any application in freq/harmonics measurement? If so how?
What is difference between Harmonic and Non harmonic Capacitor Bank?
What should be current in the Primary and secondary side of 1000KVA (11KV Supply)Transformer.?
How to calibrate or test an LT Air Circuit breaker 440 volts, 35 KA, 800 Amps ?