what is the formula to find Amp. for an 3 phase moter both if H.P. or if kW is known?
Answers were Sorted based on User's Feedback
Answer / tripathi
The formula for three phase power is p=root3*v*i*cos(fi)&
voltage gernally 415V & power factor is given in motor name
plate & kw is also mention in name plate.So u can calculate
current easily.if the power is given in H.P then multiplied
by .746.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / shahebaz shikh
as we know that the formula of power is root
3*voltage*current and hence
current=power/(root3*voltage)=746*power/(root3*voltage)
| Is This Answer Correct ? | 0 Yes | 3 No |
What is meant by vector group
0 Answers GPSC Gujarat Public Service Commission, VA Tech Wabag,
Why 11KV PT Secondaries [(11000/1.732)/(110/1.732)/ (110 / 3)]are in star connection ? And why the same should not be in delta ?
what will happen if earth of 33 kv cable (earthed system) is not connected to earthing pit?
in one substation we have two power transformers of 100mva,75mva capacity.statoin load is155mva.how much each tranformers share the load????
6 Answers TNEB Tamil Nadu Electricity Board,
What is trip and closing coil in cb? Why need of them
what will be the effect on the voltage .if power frequency is increasing or decreasing.
Let's say I have 2 current carrying conductors C1 and C2 carrying currents of 5A and 10A. They are brought close to each other from a distance of infinity to a distance of 10cm away from each other - 1. What would be the values of current flowing in each conductor when (taking into account effects of interference of each conductor on the other) - a. The currents are AC b. The currents are DC c. C1 is AC and C2 is DC Please explain your answer with mathematical equations and formulas. Please specify the final numeric answer. Please make assumptions and clearly specify them.
why steady state stability limit is greater than transient stability limit ? How it can be explained ?
how we findout a ignater is faulty or not?
We are planning to synchronized DG's with our captive plant in the event of black start of plant, but before sync we checked voltage of DG with our plant voltage and it varies from 5 V to 450 V. So in this condition how we can sync DG with plant ?
What is the effect on Power factor and capacitor when your company load is more than 70 % of welding transformer
how can we calculate the ampacity of the electrical wire/cable. and what are the factors must be considered. pls. elaborate.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)