what are the difference between protection class CT and
Class PS CT
Answer Posted / patel indukumar
Protection class is ued in protection like over current
relay and earth fault relay of transformer,Alternator and
HT motor.PS class is used in DIfferential protection like
transformer,Alternator and HT motor.
| Is This Answer Correct ? | 13 Yes | 6 No |
Post New Answer View All Answers
how to meas-our losses for L.T & H.T
Which power will flow first if we switch on a motor Active or Reactive? How?
why it is not advisable to run low rating (19KVA) DG sets in parallel for long durations even though they are provided with droop ckts (QDC)
What are the main faults of DC generators?
WHAT IS MEANT BY TV TERMINAL IN 500MVA TRANSFORMER?
In case of salient pole alternator when number of poles are 4 or more than 4 it helps the flux wave to be sinusoid as air gap length is increased from center to tip , but if the number of poles are 2 how does the flux wave is sinusoidal?
pls tell me about ups internal connection & we have given only 3 phase supply to ups system how get 4 wire (R Y B N )
How many types of circuit loads are there in a common electrical circuit?
What is the instrument to check the rotating diode fuse of alternator in running conditions?
IF alternator SCR value will be high means what happen in alternator efficency at operating power factor of 0.8
what do you mean by every IC 74 first digit.why are you using this no.why not using another no.
The magnitude of sum of two sinusoidal av voltage is equal to 230 volt.the magnitude of each individual voltage is also equal to 230 volt.what must be the phase difference between voltages?
what is mind in cable
what is difference between bus coupler and auto transfer switch
can we synchronize star system generators with delta system generators?