what is the purpose of NGR?
Answers were Sorted based on User's Feedback
Answer / ajay kumar
NGR MEANS NUTRAL GRAUNGING RESISTOR WHICH IS CONNECT TO
STAR POINT OF TF&ALTRNATOR WHICH WORK TO BALANCE THE AXESS
CURRENT IB THE UNBALANCE CONDITION AND ALSO EARTH FALT
ACCURE IN IN MACHINE THR CURRENT SLITLY GROUND THROUGH IT
AND PROTECT THE MACHINE . IT IS USED UP TO 11KV SYSTEM
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / vaibhav patil
NGR means neutral grounding resistor.it is use to limit the
foult current in abnormal condition.it have resistor bank
which limit the plant current but not fault current.earth
fault CT is also mount at this for protection against earth
fault.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / tirupathi
ngr improoves stability of alternator when ever fault
current flows through it and it improves steadystate
stability limit for synchronous power transmission
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k. venkateswara sastry
NGR is used in HT generators only. This is to control the earth fault currents occurred in Generator so as to limit the damage of Core of the Generator. If core gets damaged, the total generator gets wasted.Hence it is necessary to limit the damage of core. The damage is basically done due to Earth fault Current. Current is the element any where in Electrical system to generate heat and over heat damages.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / avinash kumar
NGR means neutral grounding resistor.It is used to limit
the earth fault current.generally the NGR used upto the 11kv
Ac system.The function of NGR is to protect the equipments
against the earth fault , help to limit the fault current to
earth.Its also give the additional purpose to maintain the
balance current in all three phases w.r.t neutral . Its also
give the additional purpose to maintain the balance voltage
between all three phases w.r.t neutral .
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ajay yadav
N.G.R. IS THE NUTRAL GRAUNDING RESISTENCE WHICH IS
INSTALLED ON THE OUTPUT OF POWER TRAFO. OR ALTERNATORS AS
WELL. IT PROTECT THE TRAFO. OR ALTR. FROM THE FAULTY
CONDITION BY GROUNDING THE ACCESIVE CURRENT DUE FAULT.
IT'S ALSO PROVIDE THE RELIABLE OPRATION IN UNBALANCE
CONDITION by GROUNDING THE UNBALACE PHASE CURRENT.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / er. avijit dixit
NGR means neutral grounding resistors....it is just used for
the purpose of solidly grounding arrangement of star
connected 3.3 kv to more stator winding of alternator. NGR
IS USED WITH A HIGH RESISTANCE FOR ABOUT 65.5 OHMS IN FOUR
PARTS MEANS 63.5*4 IS THE TOTAL VALUE. IT LIMITS THE NEUTRAL
CURRENT UP TO THE SPECIFIED CT RATIO AND ALSO PROVIDES A
DIFFERENTIAL PROTECTION TO THE STATOR WINDINGS OF
ALTERNATOR. NGR IS ALSO USED TO PREVENTS THE EARTH LEAKAGE
STRAY CAPACITANCE AND STOPS THE REVERSE SURGES. IT PROVIDES
PROTECTION TO THE PROTECTIVE CTS AND PTS AGAINST HEAVY
EARTH CURRENT FLOW DURING STABILITY LOOSE.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / subodh jain
NGR stans for neutral ground resistor...
it is sometimes also called NGT..neutral ground transformer
its purpose is to dissipate extra unbalance current that flows
into any winding in form of heat..rather than just connecting them to ground
| Is This Answer Correct ? | 1 Yes | 1 No |
NGR(Neutral Ground Resistor) which is connected at the star point of an
alternator ... N.G.R PROTECT TO ALTERNATOR WE ARE USE C.T. IN N.G.R.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / yogesh patil
neutral grounding resistor is used for the protection of
transformers , alternators & other costly equipments in the
system, when any fault occurs in the system , system
becomes unbalanced, NGR limits the fault current to give
the enough time to the protection circuit to operate
| Is This Answer Correct ? | 7 Yes | 8 No |
What is P.F? Formula for calculating PF in HT side?
sir, my question is that if we start any three phase induction motor with star connection.will be current taken ? please send a formula.
If a 1.5V,3W torch light bulb is connected in series with a 15HP/11.19KW,230V single phase motor and the combination is connected against a 230V supply and switched on than what will happen keeping all other parameters as it should be A)the bulb will glow normally B)the bulb will not glow C)the bulb will glow with extra brightness D)the bulb will burn out and if a fuse is connected to the above circuit will something happen to the fuse and what about the single phase motor will it be affected? Please explain with derivation
Why stand-by earth fault relay and restricted earth fault relays are connected between neutral and ground in transformer?
If a contactor need to replace with faulty one. what I want to check?
if a damaged 500kva transformer with %impedance 2.6 is replaced by two transformers of 250Kva with different % impedance will they be able to catter the load. what will be the ratio of load on the two transformers if the % impedance is in the ratio 1:2
which transfofrmer oil break down voltage strength get will be more if oil sample taken from bottom of tank or oil sample taken from top of the transfomer tank.
what a function diesel generetaor turbo charger & turbo charger is more heated explain reason ?
Do we really need wheels for the transformer
how we can to the synchronization in transformer. What are the conditions for that.
16kv transformeris stolen in my village.and department is not taking action.then what should i do.any shortcut .please help any idea
Are Refrigerators & Deep Freezers the Inductive load ? How to calculate the Power Factor & hence the Output Power for them ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)