what is the difference between megger and earth tester?
Answers were Sorted based on User's Feedback
Answer / m.nandhini
WE CAN MEASURE THE INSULATION RESISTANCE OF DC MACHINE AND
AC MACHINE BY USING INSULATION MEGGAR.IT SHOULD BE OF THE
ORDER OF MEGA OHMS..
EARTH RESISTANCE IS THE RESISTANCE OFFERED
BY THE SOIL.IT SHOULD BE OF ORDER OF OHMS
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / yenkatachalm
Megger is used for measuring an insulation resistance of
motor winding of cable etc. which is measured in megaohm.
While earth tester has earth electrodes which are used to
measure eathpit resistance & it is measured in ohm.
megger is used for measuring insulation resistance in mega
ohm range ,while earth tester is used for measuring the
earth resistance which is always less than 5 ohms ie a low
resistance
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / surabhi soma sekhar
megger is nothing but an insulation tester, used to measure
(during off-line)the insulation resistance between two
conducting paths and/or a conducting path and a earth,and
usually in MOhms, whereas, an earth tester is an instrument
used to measure the earth resistance with the help of earth
electrodes and usually in Ohms
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / shahid
megger is trade name of instrument and used for IR value and
earth tester is used for test the ground conductor
resistance if u see all same but earth tester 3 wire.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / muhammad sherif e s
megger is an instrument which is used for the measurement of
insulation of a particular object . the principle of
ratiometer ohmmeters is particularly used in meggers.
while the earth tester is used for measurement of earth
resistance which will be less than 5ohm
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / saumya ranjan lenka
<1>Megger=Meggar megger means insulation resistance(IR VALUES) of any cable ,wire bus bar etc .ITS UNIT IS OHM
<2>
It only measure earth resistance of pit.ITS UNIT IS OHM.
It has two electrode (i.e potential electrode and current electrode) with respect to earth plate under test. The potential electrode will fixed 15mtr from earth plate under test and current electrode 30mtr from earth plate under test.
<3> IF WE ROTATE THE HANDLE OF EARTH TESTER IN OPEN CONDITION THEN THE READING WILL BE 0 OHMS. BUT MEGGER WILL SHOWS INFINITE OHMS.
<4 >MEGGER HAS THREE TERMINALS <i>LINE
<ii> GUARD
<iii>EARTH
<5>EARTH TESTER HAS THREE TERMINAL <i>E(earth plate under test) <ii>P(potential electrode ) <iii>C( current electrode)
BY ER.SAUMYA RANJAN LENKA, STERLING AND WILSON LTD ,DSP SITE WEST BENGAL
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / abel tamang
megger is an electrical instrument which measures the resistance of the insulation whereas earth tester is also an electrical instrument by which we measure earth resistance...
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ashish
The term of earth resistivity expressed in ohm centimetre is one basic variable affecting resistance to earth of an electrode system, The megger is measuring an insulation resistance between any phase & earth or ground where as earth tester is used.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / er vimal
Megger is a ratio type instrument which insulation resistance measured in mega ohm
Earth tester is a indicating type instrument which earth resistance measured in ohm between two point
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kabir0921
Originally The term Megger is wrong.Megger is the name of company.
Is This Answer Correct ? | 10 Yes | 11 No |
Single phase and threephase power calculation
WHY AIR COMPRESOR IS STARTED UNLOADED
sent to a site and asked to explain how you would like a twenty seven flour building should be supplied with lighting and sockets plus a water boiler.
why we calculate only 11kv 33kv and 132kv ... why not 10kv 20kv 45kv?
watt meter have 4 terminals what there name??? and what theses 4 terminals indicates ?? and why 2 terminals are short circuited??
Maximum efficiency occurs in electrical machines is at i)Full load,ii)50% of full load,iii)Near full load,iv)None of these
what is the voltage level which is used in transformer short circuit test
Why we Specify Transformer rating 433 V Instead of 415V ?
why 3 phase is converted into 2 phase using electronics circuit why not 2 phases are diresctly putted from the 3 phase transformer??
if 40 watt bulb has higher resistance then a 100watt bulb then according to joul farmula p=I^2R the 40 watt bulb more power consume then 100 watt bulb.
In zero voltage we can pass supply to our body means we cant get shock its true ? how we can do it ?
what use marshalling kishock in power transformer?