what is the difference between megger and earth tester?
Answer Posted / surabhi soma sekhar
megger is nothing but an insulation tester, used to measure
(during off-line)the insulation resistance between two
conducting paths and/or a conducting path and a earth,and
usually in MOhms, whereas, an earth tester is an instrument
used to measure the earth resistance with the help of earth
electrodes and usually in Ohms
| Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
Difference between field rheostat and armature rheostat.
Define what is the function of anti-pumping in circuit breaker?
how to calculate the step resistance for slipring induction motor,how you deside the no of step for that?
What is the meaning of HT Trivector Meter ?
I need a formula to calculate the size of cable as per load but in the terms of length. Please Reply me as i search lot of sites but i did not get the answer.
Can 4pole (3 phase+neautral )RCCB proper functioning in only 3 phase load (no neautral, no Earth) ?
Could Please Explain briefly. Why used stabilizing resistance series with High impedance bus differential protection relay.
Explain Circuit Breaker Trip Characteristics in detail.
what is kvarh? Please define it With calculation General motors ?
before transformer oil dielectric strenght tests are taken the oil should be allowed to settle to remove option 1 air bubbles 2 gasses 3 contamination 4 water
how to synchronize 3 phase slip ring induction motors of different ratings.
Define corner frequency?
In dc ckt. 24v or 110v, which one is more efficient and why?
any earth foult trip the relay but in welding time not trip by earth foult
describe the Tranformer testing procedure