When in a large power system if the demand of power is
larger than the generated power the frequency of the power
system drops.(assume the rated frequency is 50Hz and now it
is 49Hz)
So does this mean the demand is totally supplied with a
lower value of generated power in a lower frequency?
Answer / k.prakashchandra
Demand is always equal to generation at a steady
frequency.When frequency drops the demand/load also drops
automatically.If not, frequency goes on dropping till shut down.
| Is This Answer Correct ? | 0 Yes | 0 No |
in single phase circuit if i connect a heater between phase and neutral, then what will be the current path? phase to neutral or neutral to phase.
Define peak time.
Dear sir, How to calculate 3.5 core pvc aluminium armoured cable meter wise carrying amps rating.Please give the solution with a good example.
why rating of motor in HP?
how to check dc current,how to fix ammeter in dc line
What is encoder, how it function
110 KW MOTER DOL STATER 240SQ.MM CABLE MOTER AND STARTER DISTANCE IS 110 METER WHAT IS VOTAGE IN MOTER END AND SYSTEM VOTAGE IS 415 V HOW I CAN CALCULTE
Define damping ratio.
how to calculate energy meter multipling factor by ct & pt raitio
do we convert single phase line to three phase at minimum cost?
at work i have a genertor/alternater what is the easyest way to work out if it is dc or ac?
In our homes we place the 5Amps fuse...now in our house only takes 5Amps for all normal conditions ha???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)