how and where megger works?
Answers were Sorted based on User's Feedback
Answer / vijaykumar shetye
A megameter, or a Megger as it is commonly called, is used
to measure the insulation resistance of cables and other
electrical equipment. The measured value is in mega ohms.
Hence the term Megger.
Most meggers generate 500 Volts DC supply, but their
current capacity remains low.
When the two terminals of a megameter is connected to
across the equipment to be tested, the high voltage gets
leaked into the equipment. The resistance is inversely
proportional to the current flowing through the equipment
under test.
Originally, most meggers were analog in nature, and were
generating high voltage using a dynamo, when the lever is
rotated at high speed.
Today most meggers available are digital, and can
generate 500 volts as well as 1000V. Some meggers have
winding resistance testing facility as well, and hence can
be used as a single tool to test the resistance of a motor
in ohms as well as in Megaohms.
Meggers used for checking high resistance like that of
mains transformrs, generate much higher voltages and are
generally analog type.
Is This Answer Correct ? | 113 Yes | 2 No |
Answer / anusha reddy.m
Megger is used to find the insulation resistance .
Is This Answer Correct ? | 122 Yes | 46 No |
Answer / iraikhan
megger is a device with a hand driven dc generator and
direct reading ohm meter for testing the insulators in
other words its resistance
Is This Answer Correct ? | 45 Yes | 37 No |
Answer / k.babu
Megger inbuilted inside a dynomo which is used to energise
the system. Which is used to find the Earth Resistance
Is This Answer Correct ? | 42 Yes | 47 No |
Answer / meghraj kabdule
Friends Megger is mfg. company which first find out the IR
tester for the measurment of insulation resistance.
Is This Answer Correct ? | 15 Yes | 31 No |
Answer / deepak kumar
megger is generally used for measuring the high resistance,hence it reffer as the megger mens it can measure the 500 mega ohms.it is used for testing the o.c and s.c test.it is combination of generator and direct ohmmeter.the speed of the megger is kept at 160 r.p.m.there are three range of megger.
1-300 v
2-750 v
3-1000 v
Is This Answer Correct ? | 4 Yes | 23 No |
Answer / shibukp22
megger testing tow type conducter to counducter and
counducter to earth
Is This Answer Correct ? | 1 Yes | 24 No |
Answer / ashwin
Go through the contents of this link:
http://en.wikipedia.org/wiki/Megger
Is This Answer Correct ? | 4 Yes | 28 No |
when the PFR (POWER FACTOR REGULATOR)change a step to zero,one of the RCCB will triped off,is it the changing step of this PFR effect the RCCB?
1. what is the power factor and whatis his losses 2. what is the working procedure of 51RNB AND 87 relay
-What should be minimum value of insulation resistance and maximum value of earth resistance at any electrical instillation and what is method of testing the same.
What is the difference between MCB and Earth MCB? What is the working principal of MCB?
If two induction motors A and B are identical except that the air-gap motor 'A' is 50 % greater than that of motor 'B', then
where would be tap changer in transformer & why?
I want to know if it is possible to use Variable Frequency Drive to reduce the current required for starting a motor?
why in the three pin plug all 3 pins are cutted ?
Residual voltage & residual current used in which protection?
5 Answers Qatar Gas, Reliance, Transformers and Electricals,
Which Current transformer will be bigger in size, 400/5 or 400/1 & why?
HRC fuse provide best protection against
Dg pf .71 i am improve pf 0.80 what capacitor connected in dg how?
0 Answers AVT Natural Products, EMC,