In transformer how measure the winding temperature ?
Answers were Sorted based on User's Feedback
Answer / ambat
The transformer winding temperature measurement is a
complicated procedure since we cannnot place any sensor on
the surphase of the winding.So normally a WTI CT is
connected with suitable ratio and the secondary current is
used to heat a resiistance kept inside the thermowell
filled with the same oil.the resistance used for this will
be of the same thermal characteristic of the transformer
winding wire to get the thermal image.Then temperature of
the heated oil is measured by using RTD or any other
temperature measuring device.SO many other elctronic
devises are also now available. but in all devices WTI CT
are essential
| Is This Answer Correct ? | 31 Yes | 0 No |
Answer / mohamed
how to select the CT ratio for WTI
the answer :
SCIENTIFIC CONTROLS Mechanical Instruments are incorporates
proven design features acquired from many years of
experience in providing Temperature Indicators/Controllers
for Power & Distribution Transformers.
Oil Temperature Indicator: The Oil Temperature Indicator
(OTI) measures the Top oil Temperature. It is used for
control and protection for all transformers.
Winding Temperature Indicator: The Winding is the component
with highest temperature within the transformer and, above
all, the one subject to the fastest temperature increase as
the load increases. Thus to have total control of the
temperature parameter within transformer, the temperature
of the winding as well as top oil, must be measured. An
indirect system is used to measure winding temperature,
since it is dangerous to place a sensor close to winding
due to the high voltage. The indirect measurement is done
by means of a Built-in Thermal Image.
Winding Temperature Indicator is equipped with a specially
designed Heater which is placed around the operating
bellows through which passes a current proportional to the
current passing through the transformer winding subject to
a given load. Winding Temperature is measured by connecting
the CT Secondary of the Transformer through a shunt
resistor inside the Winding Temperature Indicator to the
Heater Coil around the operating Bellows. It is possible to
adjust gradient by means of Shunt Resistor.
In this way the value of the winding temperature indicated
by the instrument will be equal to the one planned by the
transformer manufacturer for a given transformer load.
| Is This Answer Correct ? | 22 Yes | 1 No |
Answer / arvind
if the transformer is oil cooled then temperature is
measured by dipping thermometer to the top oil.And if ithe
xformer is aircooled then it is measured by resistance
method.
| Is This Answer Correct ? | 17 Yes | 5 No |
Answer / shiva
sumpenrs test is also used to find the temp rise of the
transfrmers.
| Is This Answer Correct ? | 1 Yes | 7 No |
Answer / vikram
it is easy to find the temperature of the transformer
winding by BUCHHOLZ RELAY and also with the THERMAL RELAY.
ALSO WE CAN SET THE LIMITS OF THE TEMPERATURE FOR SAFETY.
| Is This Answer Correct ? | 4 Yes | 31 No |
what should be the resistance between two winding. Let 10 kw motor
For example, if I use Star delta transformer for distribution, Can I Connect 230 V lighting load bewteen secondary phase & primary neutarl. What will be the effect, if I connect in this manner?
Wat is meant by OLTC?
show the physical connection and phasor diagrams of 1: DZO 2: Yd1 3: DZ6 4: Yd11 5: YZ11
1.what is surge 2.what is lightning 3.what is switching 4.difference between surge,lightning,switching used in power system 4.definition of surgearrestor,lightningarrestor 5.adv and disadv of surgearrestor,lightningarrestor 6.uses and purpose of surgearrestorand lightning arrestor 7.block dia of surge arrestor 8.blockdiagram of lightning arrestor 9.operation and working of surge arrestor and lightning arrestor 10.basic formula of surgearrestor and lightning arrestor 11.basic diagram of surge arrestor and lightning arrestor
1 Answers Crompton Greaves, Framo, L&T,
Can we parallel lise the secondary side of the two similiar transformers with same voltage ration, imp, but with different vector groups.. ( for ex. 11 KV / 6.6KV two trfs but different vector groups can we parallelise both of them ,, what happens if we parallelise them
difference between fleming's left hand rule and RHR briefly.
how to calculate power factor of capacitor? what is transformer rating?
how to calculate the powerfactor in induction motor having name plate details? for example 1 h.p motor 1.86 A 415 V
What is the role of a Production Engg in a Industry?????
When MICC cables used ?
1.what type of wave is produced from i.online ups ii.offline ups iii.inverter.why don't we use inverter instant of offline ups for computer,what's the reason?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)