In transformer how measure the winding temperature ?..

Answer / ambat

The transformer winding temperature measurement is a
complicated procedure since we cannnot place any sensor on
the surphase of the winding.So normally a WTI CT is
connected with suitable ratio and the secondary current is
used to heat a resiistance kept inside the thermowell
filled with the same oil.the resistance used for this will
be of the same thermal characteristic of the transformer
winding wire to get the thermal image.Then temperature of
the heated oil is measured by using RTD or any other
temperature measuring device.SO many other elctronic
devises are also now available. but in all devices WTI CT
are essential

Is This Answer Correct ?    31 Yes 0 No

In transformer how measure the winding temperature ?..

Answer / mohamed

how to select the CT ratio for WTI
the answer :
SCIENTIFIC CONTROLS Mechanical Instruments are incorporates
proven design features acquired from many years of
experience in providing Temperature Indicators/Controllers
for Power & Distribution Transformers.
Oil Temperature Indicator: The Oil Temperature Indicator
(OTI) measures the Top oil Temperature. It is used for
control and protection for all transformers.
Winding Temperature Indicator: The Winding is the component
with highest temperature within the transformer and, above
all, the one subject to the fastest temperature increase as
the load increases. Thus to have total control of the
temperature parameter within transformer, the temperature
of the winding as well as top oil, must be measured. An
indirect system is used to measure winding temperature,
since it is dangerous to place a sensor close to winding
due to the high voltage. The indirect measurement is done
by means of a Built-in Thermal Image.
Winding Temperature Indicator is equipped with a specially
designed Heater which is placed around the operating
bellows through which passes a current proportional to the
current passing through the transformer winding subject to
a given load. Winding Temperature is measured by connecting
the CT Secondary of the Transformer through a shunt
resistor inside the Winding Temperature Indicator to the
Heater Coil around the operating Bellows. It is possible to
adjust gradient by means of Shunt Resistor.
In this way the value of the winding temperature indicated
by the instrument will be equal to the one planned by the
transformer manufacturer for a given transformer load.

Is This Answer Correct ?    22 Yes 1 No

In transformer how measure the winding temperature ?..

Answer / arvind

if the transformer is oil cooled then temperature is
measured by dipping thermometer to the top oil.And if ithe
xformer is aircooled then it is measured by resistance
method.

Is This Answer Correct ?    17 Yes 5 No

In transformer how measure the winding temperature ?..

Answer / shiva

sumpenrs test is also used to find the temp rise of the
transfrmers.

Is This Answer Correct ?    1 Yes 7 No

In transformer how measure the winding temperature ?..

Answer / vikram

it is easy to find the temperature of the transformer
winding by BUCHHOLZ RELAY and also with the THERMAL RELAY.
ALSO WE CAN SET THE LIMITS OF THE TEMPERATURE FOR SAFETY.

Is This Answer Correct ?    4 Yes 31 No

Post New Answer

More Electrical Engineering Interview Questions

what is the formula to find battery back up of ups?

3 Answers  


When will you multiply and devide with derating factors to the actual value while sizing the cable?

0 Answers  


what is the difference between 4pole & 6pole DC Motors & give advantage ?

0 Answers  


What is balance beam relay ?

2 Answers   Roman,


if dc is better then ac...then why we are perfering ac over dc?eg:at home?

2 Answers  






show the physical connection and phasor diagrams of 1: DZO 2: Yd1 3: DZ6 4: Yd11 5: YZ11

0 Answers  


depending on what we can choose the rate of mccb considering that we know the total load

2 Answers  


WHAT DO YOU MEAN THE DIFFERENT TYPE OF CURVES OF RELAY LIKE STANDARD INVERSE, VARY INVERSE, NORMAL INVERSE, LONG INVERSE ETC....

0 Answers  


If the rotor pf of a 3 phase induction motor is .866, then what is the phase displacement between stator and rotor magnetic field 1)30,2)120,3)150,4)90 please justify....

2 Answers   GATE,


Compare salient pole and cylindrical rotor machines.

0 Answers  


Please specify the parts of VCB&ACB

1 Answers  


In view of Electrical Engg. What is the use of SCR(Silicon control rectifier)

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)