Answer / ..................
when we say that DG set has 0.8 Power Factor it means
a 1000kVA DG shall deliver 800Watts only.
If we try to load more than this it shall drag more amount
of current. & Ultimately voltage will drop accordingly
resulting in generation of capacitive VARs.
| Is This Answer Correct ? | 8 Yes | 5 No |
Most DG's are rated at 0.8 PF. They do not have to operate
at this PF but certain considerations must be taken into
account when the PF is changed.
1 - The kw available is only 80% of the kva rating. This is
limited by the output of the engine. If the load is at
unity PF the output is only 80% of the kva rating.
Otherwise the engine is overloaded.
2 - The maximum current the alternator windings are
designed to carry is the current at the kva rating. If the
PF is below 0.8 the kw load must be reduced to make up for
the extra kvar load so the kva is not above the rated
maximum.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / premkumar
Normal to Design DG p.f is 0.8, some person say Dg set to use APFC with Dual sense Relay for EB and DG side to improve the DG efficiency. Its wright or Wrong.
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / thowsif_emerson
Fristly the design Power factor of the DG set is 0.8, i.e.
capacity of the DG can be used 80%, If you run the DG set
on higher power factor then DG set run on more excitation
due the more excitation the DG set goes to the Capacitive
load when the DG set run capcitve load then current lead to
the voltage. This is the losses of power.
| Is This Answer Correct ? | 13 Yes | 17 No |
Answer / sree
Generally at what power factor, DG sets in generating
stations operate ? presuming that the generators run at
0.8 PF, I think it is a loss. what do say?
| Is This Answer Correct ? | 4 Yes | 13 No |
is there a different b\w ground fault CB and earth leakage
what is the formula for transformer oil?
what is tandem isolator ??????????
What are the protections used in a HT breaker to protect the HT motors.
Please give me a erda placement paper
IS THERE ANY ELECTRONIC CIRCUIT TO REDUCE THE NEUTRAL TO EARTH VOLTAGE BELOW 3V ?
1.Why hydrogen used for cooling in generators 2.Why electrical equipment protected by ground 3.Why earthing for transmission line 4.What is rms value of half wave rectified square wave. If Rms value of actual wave 2amps.
how the direction relay sense rhe directional fault?it's forward or reverse?
how meger function
in the directional overcurrent and earthfault protection,normally we are setting the angle 45 deg lead for phase fault overcurrent and -45 deg lead for earthfault fro forward direction.but both the fault are operating on the same angle region only.why?how the relay will response?
Why HT voltages are expressed in 11KV,22KV,33KV and so on? (ie in times of 11)
Why a Transformer Noise during its running condition ??
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)