Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


1KVA transformer of different frequencies of
50hz,100hz,500hz&1000hz. which one of these transformer has
big size? Give reason

Answers were Sorted based on User's Feedback



1KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these trans..

Answer / kishore

X(1 KVA) 50 HZ n Y(1 KVA ) 500 HZ
E = 4.44 f * FLUX * N
that is emf durectly proportional to flux which is f*B*A
B- flux density n A= area of c/s of transformer

as KVA reting of both are same n hence
X (f*B*A) = Y (f*B*A)
as frequency of X is smaller than Y so area of c/s of X
must be larger
hence 50 HZ transformer is largest and so on

kishoresahoo@ymail.com

Is This Answer Correct ?    39 Yes 8 No

1KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these trans..

Answer / bhanu(secure meters ltd.)

due to some mechanical constraints, generally transformer
size is inversely proportional to the operating frequency.

thus 50 hz, transformer will have max.size.

Is This Answer Correct ?    18 Yes 3 No

1KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these trans..

Answer / asutosh

with increase in frequency the size decreases so the 50 hz
will have big size
for better understanding refer high frequency transformers

Is This Answer Correct ?    15 Yes 3 No

1KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these trans..

Answer / ambi

this is a short cut method based on analysis..
generally power transformers use lower frequncy(50hz) and
we know in electronic ckts like oscillators producing very
high frqs in range of KHz we use only SMALL trfrs than pwr
trfrs.... so on analysing we can conclude tat higher
frquency transformers have less volume...
NOTE: this is only shrt cut mthd, actual reason depends on
the FORMULA only for determining the size

Is This Answer Correct ?    9 Yes 1 No

1KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these trans..

Answer / chankey garg

while increasing freq width of stamping decreases so 50hz
having bigest size

Is This Answer Correct ?    11 Yes 4 No

1KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these trans..

Answer / mohd shahid

bhai kishore see here we r talking about same KVA rating
not same KV rating.
here you r equting the KV rating(ie by equating the induced
emfs)
there is a diff between kv and kva hence kindly refer again
to your solution which acco. to me is not correct

Is This Answer Correct ?    8 Yes 3 No

1KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these trans..

Answer / rahul

The EMF of a transformer at a given flux density increases
with frequency.By operating at higher frequencies,
transformers can be physically more compact because a given
core is able to transfer more power without reaching
saturation and fewer turns are needed to achieve the same
impedance.

So, 50Hz transformer will be the bigger one.

Is This Answer Correct ?    5 Yes 0 No

1KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these trans..

Answer / r k alaria

The impedance of the transformer is greater for higher frequencies (as X=wL). So for constant voltage to keep same current rating (because for constant kVA)we have to reduce the inductance of the winding. And to reduce the inductance we have to reduce the no. of turns in the windings of the transformer. By reducing the no. of turns the size of the transformer will be reduced for higher frequencies.

Is This Answer Correct ?    6 Yes 1 No

1KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these trans..

Answer / engr. ziaul ashraf shafi

Mohd Shahid,
From the eqn V/F= flux, you wrote that "increasing the
frequency will cause the flux increasing. HOW ??

Is This Answer Correct ?    4 Yes 1 No

1KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these trans..

Answer / ganesh.m

Consider the primary of a transformer is operating at 230V,
50Hz. Consider the the secondary of the same transformer
generates 12V, 50Hz. What will happen to the secodnary
voltage, if the primary is fed with 230V,1KHZ supply?

Is This Answer Correct ?    5 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

Current Transformer's star point must face the protected object for the relay operation?

2 Answers   Siemens,


electromechanical relay type identification example : type=tjmh t-stants for j- m- h-

0 Answers  


why voltages are multiple of 11 or 1.1???describe with derivation plzzz.thanks

2 Answers  


What is the name of transformers oil filteration equipment?

0 Answers   Reliance,


What is tan delta point of transformer?

2 Answers  


I have 2 transformers in two different plants, both are without OLTC but i am facing problem of voltage fluctuation at LV side from only one transformer. i have to change its taps manually twice in a day. Another transformer delivering voltage is ok. Please guide me about the problem

1 Answers  


what is the acb tripping & closing voltage.

2 Answers  


1) name the communication cable and how it is communicate in between plc to modbus , plc with hmi? 2)name of the communication cables?

1 Answers  


exact definition of reactive power in power system

2 Answers   Sreetech,


Why in earthing, the earthing plate is put in vertical position? and further what is soft coke that is used in earthing?

3 Answers   Wipro,


We have 2 Nos. Transformer with the capacity of 2000KVA and 1250 KVA and currently using only one 2000KVA T/R during operational hours while non- operational hous 1250 KVA T/R also used to reduce T & D losses. Similarly, 2 capacitor bank of 500KVAR and 300 KVAR also installed to balance reactive power. Now problem is around 1000 KW load PF is not maintaning 0.99 as 350 KVAR capacitor is in healty condtion. Now the PF is maintain 0.95 to 0.96.

2 Answers  


why we use four type of phase angle difference between pimary & secondry winding of a transformer & where we use them?

0 Answers   Grasim,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)