1KVA transformer of different frequencies of
50hz,100hz,500hz&1000hz. which one of these transformer has
big size? Give reason
Answers were Sorted based on User's Feedback
Answer / kishore
X(1 KVA) 50 HZ n Y(1 KVA ) 500 HZ
E = 4.44 f * FLUX * N
that is emf durectly proportional to flux which is f*B*A
B- flux density n A= area of c/s of transformer
as KVA reting of both are same n hence
X (f*B*A) = Y (f*B*A)
as frequency of X is smaller than Y so area of c/s of X
must be larger
hence 50 HZ transformer is largest and so on
kishoresahoo@ymail.com
| Is This Answer Correct ? | 39 Yes | 8 No |
Answer / bhanu(secure meters ltd.)
due to some mechanical constraints, generally transformer
size is inversely proportional to the operating frequency.
thus 50 hz, transformer will have max.size.
| Is This Answer Correct ? | 18 Yes | 3 No |
Answer / asutosh
with increase in frequency the size decreases so the 50 hz
will have big size
for better understanding refer high frequency transformers
| Is This Answer Correct ? | 15 Yes | 3 No |
Answer / ambi
this is a short cut method based on analysis..
generally power transformers use lower frequncy(50hz) and
we know in electronic ckts like oscillators producing very
high frqs in range of KHz we use only SMALL trfrs than pwr
trfrs.... so on analysing we can conclude tat higher
frquency transformers have less volume...
NOTE: this is only shrt cut mthd, actual reason depends on
the FORMULA only for determining the size
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / chankey garg
while increasing freq width of stamping decreases so 50hz
having bigest size
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / mohd shahid
bhai kishore see here we r talking about same KVA rating
not same KV rating.
here you r equting the KV rating(ie by equating the induced
emfs)
there is a diff between kv and kva hence kindly refer again
to your solution which acco. to me is not correct
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / rahul
The EMF of a transformer at a given flux density increases
with frequency.By operating at higher frequencies,
transformers can be physically more compact because a given
core is able to transfer more power without reaching
saturation and fewer turns are needed to achieve the same
impedance.
So, 50Hz transformer will be the bigger one.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / r k alaria
The impedance of the transformer is greater for higher frequencies (as X=wL). So for constant voltage to keep same current rating (because for constant kVA)we have to reduce the inductance of the winding. And to reduce the inductance we have to reduce the no. of turns in the windings of the transformer. By reducing the no. of turns the size of the transformer will be reduced for higher frequencies.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / engr. ziaul ashraf shafi
Mohd Shahid,
From the eqn V/F= flux, you wrote that "increasing the
frequency will cause the flux increasing. HOW ??
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / ganesh.m
Consider the primary of a transformer is operating at 230V,
50Hz. Consider the the secondary of the same transformer
generates 12V, 50Hz. What will happen to the secodnary
voltage, if the primary is fed with 230V,1KHZ supply?
| Is This Answer Correct ? | 5 Yes | 4 No |
How can calculate the daily electrical consumption of 7.5 HP motor, if the moter runs 24 hrs continiously. Also have to know about 3.5 hp chiller.
How to size the Neutral grounding resistor?
What are the characteristics of negative feedback?
Is any generator is developed which is operated with out diesal or other expensive source?
what is the value of combined earthing in general electrical circiut?
0 Answers Cathtect Engineering,
kVA rating of open delta connected transformer is _____% kVA rating of delta/delta connection A 50 B 70.7 C 57.7 D 75.7
What are various impedence in any machine
2 Answers Engineers India Limited, NTPC,
What are the uses of stepper motor?
How to measure 20 hp motor resitance
What happens instead of using 3 phase, if we give loop of single phase to all three phases ??
If Polarization index of motor 8.75 at 500volts of medium voltage 4.16 KV motor what this mean winding good or bad pl answer if any reffrence book give me the link
why fuse is not applicable for nutral and what will happen when it applied.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)