If the supply system was 3 phase with neutral the single-
phase consumers [lighting, single-phase motors and so on]
could work [you have to check the other two phase are
disconnected at first].The current on the remaining phase
will rise since all load will stay on this single phase [it
depends on how was the load distributed per phase]. The
three-phase motor will not work at all-no start- no current
for ungrounded stator winding and high current for grounded
one].
If the supply system was 3 phases without neutral nothing
would work [you supply one-phase without return through
neutral].
| Is This Answer Correct ? | 3 Yes | 2 No |
why should we india maintain frequency of 50 Hz.
how to amps calculate from 1KVA?
what is LSR?
What are the voltage values for LT,HT,EHT and other voltages??
what is the difference SCR & TRIAC?
What is the effect of earth capacitance
What is the minimum distance between MV busbare (P to P & P to E) as per some standards
Why we connect the capacitor in Delta?if we conect in Star what will happen?
how to determine the inrush current of a transformer
Is current scalar or vector?
in control scheme dc logic wiring commonly using negative loop,what is the reason?if we use positive looping what will happen?
break down of electricity is more in summer or in winter ? give reason
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)