What is the difference between CT for protection and Ct for
metering?
Answers were Sorted based on User's Feedback
Answer / mahesh
Metering ct needs high accuracy(ie,value of metering ct should be small 0.1,0.2,etc.,) than protection ct ie, metering ct accuracy class will be=0.1,0.2,0.5,1,3 and 5
eg;
The accuracy class of measuring or metering CT is 0.1, means the maximum permissible limit of error is 0.1%, more clearly, if we try to measure 100 A with a 0.1 class CT, the measured value may be either 100.1 or 99.9 A or anything in between these range.
for protection CT the accuracy class is low (ie, value of protection ct should be high 5P,10P,15P)
| Is This Answer Correct ? | 3 Yes | 5 No |
Answer / raja
Protection CT will be more sensible then Metering CT
| Is This Answer Correct ? | 1 Yes | 5 No |
Answer / mulengal
by design protection cts have lower burden which allows for
higher fault currents while metering cts have higher burden
which allows for accuracy
| Is This Answer Correct ? | 12 Yes | 38 No |
Answer / kadiresan.k
Generally CT is used to measure higher currents, We need
both Metering and Protection CTs seperately with different
class of accuracy. The purpose of metering CT is to read
the actual current, so it has less class of accuracy.
Whereas in case of protection CT, The measured value of
current is used to protect the equipment by identifying the
abnormalities at the initial stage itself, (provided the
protection relay is tuned perfectly)and protects the
equipment(motors/transformers/transmission and distribution
systems)So it needs high accuracy than metering CTs.
| Is This Answer Correct ? | 41 Yes | 77 No |
Answer / minal
ct for protection means that current transformer is used to
step down the higher values of current to lower values
which is to be measured by the instruments.Thus it protects
the equipment from damages.
ct is also used to measure the low values of current.This
is how it is used for metering.
| Is This Answer Correct ? | 14 Yes | 124 No |
Answer / infodoss
CT is used to measure the transmission current.
Transmission currents are very high so cannot messure
directly.first to step down the current and then measure
the current using some ratio.CT protection is used to
avoide the aceident and eleminating losses.
| Is This Answer Correct ? | 37 Yes | 153 No |
Hi friends, i m electrical engineer i want a cdr for migration purpose so anybody have information about this then send me on jayesh_ee88@yahoo.com.please try to me
which has more heat effect(dc or ac)
Whats the type of current and potential transformers?
in control scheme dc logic wiring commonly using negative loop,what is the reason?if we use positive looping what will happen?
THE ROTIO OF VOLTAGE AND CURRENT IN A CLOSED CIRCUIT
12 Answers APGenco, Constant, Lanco,
WHAT IS THE REASON OF CHANGE FREQUENCY IN DG SET AFTER FULL LOAD.
What are merits & De-merits of State-Space Method? What is series programming, parallel programming, general programming & direct programming ? And, difference between these programmings Techniques ?
why h parameter are called as hybrid parameter?
Differentiate between ideal and non-ideal voltage sources?
want to know about DMRC
what is the use of vcb & isolator in substation?
What is the difference between generator and turbo generator - related to power gereration
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)