What is the difference between CT for protection and Ct for metering?..

Answer / p.raju

yes , There is difference between the protection ct and
metering CT in operating conditions

*The CT using for protection will have to carry the fault
currents which are 10 times the normal full load current
thats why it is designed at much bellow the saturation point
(knee)inorder to aviod saturation.

*The CT used for metering will have to carry only full load
current thats why it is designed near to knee point.
as per accuracy concern the metering Ct should be more
accurate under normal operating condition.....i.e under
normal operating condition the pretection CT accuracy not
imp..........

Is This Answer Correct ?    409 Yes 15 No

What is the difference between CT for protection and Ct for metering?..

Answer / avdhesh

Metering CT : It will function up to full load current only
then it will be saturated. It will not follow the CTR Above
the full load curent. Take the example of a train, if
boggies are connected to engine it will follow the speed of
engine but if coupling is broken boggies will not follow
the engine.

Protection CT : These CTs have to protect against fault
hence these CTs are not supposed to saturate during fault
current and they should transform secondary current exectly
replica of fault current. For example class 5P20 means 5 =
% error, P = protection class, 20 means = 20 times of rated
current means when 20 times of rated current is flowing
through CT the error in sec. current may be +/- 5%.

Never connect metering CT for protection purpose as it will
saturate during fault and will not provide any protection
at all.

Is This Answer Correct ?    184 Yes 16 No

What is the difference between CT for protection and Ct for metering?..

Answer / debashisdb

Two major differences:

1. Accuracy class: Metering needs high accuracy at load
current while Protection need not have that high accuracy.

2. Safety Factor: It determines the multiplicity of load
current at which the CT saturates. Metering ct should have
lesser value so that it saturates before the meters can get
damaged due to some abnormality. Protection should have
high value since its main purpose desires the ct to
withstand high fault currents to be sensed back to the
relays.

There is another special class ct that combines the
features of both the above used for differential protection.

Is This Answer Correct ?    93 Yes 12 No

What is the difference between CT for protection and Ct for metering?..

Answer / rahul

The diferrence is of accuracy class. for measuring more
accuracy is desiered

Is This Answer Correct ?    101 Yes 59 No

What is the difference between CT for protection and Ct for metering?..

Answer / amir

Metering CT: Designed at a point not far from knee point on
the CT saturation curve.
Protection CT: Designed at much lower point on the curve.

Is This Answer Correct ?    42 Yes 7 No

What is the difference between CT for protection and Ct for metering?..

Answer / john bosco

METERING CT:
these types CT are construction wise Different from
Protection CTs. Generally the Core material used will be
different and Core area will be very less compared to
protection Cts. since the application/Requirement of
metering CT is to provide Accurate current for measuremet
at normal loading condition also should saturate for
fault/abnormal condition to prevent Meters connected to
metering CTs from damages resulting from high secondary
currents on fault condition. because meters cannot
withstand for such amount secondary current.

Protection CT:
CT used for protection relays are required to provide
accurate secondary current to relay measurement for
satisfactory operation on faults.

so these CTs should not saturate on fault conditions.

Is This Answer Correct ?    26 Yes 1 No

What is the difference between CT for protection and Ct for metering?..

Answer / a.k.tiwari

metering cts are used for the urpose of measuring the current and thus recording the consumption when secondary is connected to the metering terminals.
protection cts are used for protection against over current or faulty current, their secondary is thus connected to the protection relays and the to the tripping coil. there may be series or shunt trip mechanism, thus the burden(VA) of protection ct is more as compared to metering cts.
however the accuracy class of measuring ct is of more significance as they are used for measurment.

Is This Answer Correct ?    29 Yes 6 No

What is the difference between CT for protection and Ct for metering?..

Answer / shashi kant

PROTECTION CT CORE is different as compare to Metering CT,
as metering CT SECONDARY is connected to meter to measure
so accuracy is needed ,so the core of Metering CT is
designed or made in such that its core gets saturated on
enmourse increase of primary current, for ex CT with
accuracy of 125% of rated current of ratio400:1, means its
seconary current will never go beyond 1.25amp i.e if the
primary current is 1000 amp,as by the above ratio the
secondary current should be 2.5amp, but in the case of
protection CT as its secondary is connected to relay to
sense the fault current so accuracy is not so important ,
if metering CT IS placed in place of protection ct, then in
case of any fault a heavy fault current in primary of
Metering CT the secoundary output current will be limited
to its rated current (generally 125%) which will be normal
and so the relay may not able to sense the fault

Is This Answer Correct ?    12 Yes 1 No

What is the difference between CT for protection and Ct for metering?..

Answer / arif shah

There is a very important difference between a metering CT and a protection CT. A metering CT is so designed that in case of faults, it will saturate and thus save the instrument connected to its secondary from damage due to excessive current. On the other hand, a protective CT is designed to faithfully reproduce the largest fault current.

Is This Answer Correct ?    2 Yes 1 No

What is the difference between CT for protection and Ct for metering?..

Answer / thiru

Protection ct: It is used for protection against fault in power system and also secondary connection connected to protective relay.
Metering ct: It's measure the actual current of the system and also secondary connection connected to meters.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

sail kaott diploma ece ke interviw me qus.kis parkar ke aate hai aur G.S me kya puchate hai kya sameedyaan me kis parkar ke qu.puchate hai

0 Answers   Sail,


What do you mean by transformation ratio of instrument transformer?

0 Answers  


directional relay is typically used to respond in fault condition who it can be used just as reverse power protection which purely senes direction reversal to operate a circuit breaker?

1 Answers  


How will you determine the rating of a motor for continuous duty variable load motor applications?

1 Answers  


In an ACB shunt trip coil and undervoltage coil operated normally( breaker open and charged). But closing coil not operating untill manually discharge and recharging. Any help.

0 Answers   PPIL,






why we used servo motor insted of inducation motor?

1 Answers  


what is range ACB

11 Answers  


what is diff. b/w of earth & neutral?. why we are separately using ?

3 Answers  


Two liquids hot and cold in two vessels are there and an metal bar acts as a conductor of heat between the two vessels. what happens then. what happens after 24 hrs?

0 Answers  


what is motor?

2 Answers   UIU,


Hi, i want to know is meant by power quality? How it can calculated ? How we can improve?

1 Answers  


Difference between drift current and diffusion current?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)