WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?
Answers were Sorted based on User's Feedback
Answer / laxmidhar ,nmiet bbsr
we need,
miliamp source(giving supply to i/p)
i to p converter(pressure signal to control valve)
air supply(for input to i/p and control valve)
multimeter(miliamp check)
small screw driver(for adjust zero and span)
and check
4ma for 0
8ma for 25%
12ma for 50%
16ma for 75%
20ma for 100%
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / ramkumar
We can calibrate the Controlvalve by using the mA feeder
(make-DRUCK).while calibrating the I/P using mA calibrator
error occurs adjust Zero and span in the I/P .
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / zuheir beilouni
Use a current source to calibrate the I/P converter error ,
but if the error was in the valve , calibrate the valve
positioner using Wallace and Tiernan calibration box or for
fast calibration couple a monostat gauge to calibrate and
if both were ok problem lies in the solenoid then check the
supply to it
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / biju
We can calibrate a control valve by connecting a HART/FF
communicator to the valve and then doing Autocalibration
through the instrument...
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mustafa ahmad
mA SOURCE & HART COMMUNICATOR WILL USE FOR THE CALIBRATION
OF CONTROL VALVE .WHEN U CALIBRATE THE CONTROL VALVE THAT
TIME U FOUND ANY ERROR . YOU DO AUTO CALIBRATION BY HART
COMMUNICATOR . WHEN AUTO CALIBRATION WILL FINISH , YOU DO
THE STROKE CHEK BY HART COMMUNICATOR OR mA SOURCE
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / dhanasekaran c
Depends upon the valve. Pneumatic calibrator for 0.2to
1.00kg/cm2 Valve.For Electronic positioner( 4-20ma) We can
use Loop calibrator. For Smart type of positioner fixed
valves smart calibrator 275 or 375 or 475(latest) must be
used. Field bus MC5 hand held calibrator can be used.
| Is This Answer Correct ? | 9 Yes | 12 No |
Answer / janardhan reddy
we can calibrate the control valve by using the dead weight
tester and transmitter and pid controller,
| Is This Answer Correct ? | 7 Yes | 24 No |
I HAVE PRESSURE TRANSMITTER WITH TWO WIRES 24 VOLTS SUPPLY.IF TRANSMITTER WILL GIVE SIGNAL TO THE DCS WHAT HAPPEN TO THE 24 VOLTS POWER SUPPLY IT WILL DROP OR REMAIN TO 24 VOLTS POWER SUPPLY.
Furnace draft transmitter range is -50 to +50 mmwc. why the impulse line connected in hp side?
what is mean by hot loop and cold loop testing, whts different between both
please tell me how to convert double acting ytc positioner yt-1200 into single acting ytc positioner ?
What is minimum distance between three thermocouples (2oo3) mounted on same pipe line (20")? Technically accepted by stright line mounted or circler mounted?
What is the procedure of DP switch calibration
What is difference between reset and initialization in system.
I am pujita completed Electronics and Instrumentation Engineering.As a fresher i am going to attend the interviews.Could anybody guide the topics/questions covered mostly in interviews.
What is CNC
Tr. Wiring for calibration.
tell how to calibrate a magnetic flow tx, vortex flow tx,dp flow tx,nozzle flow tx and venturi flow tx?
In dcs contol valve parameters showing like this Gain=1 or 2 , ti=7 sec, td=20sec. But temp,pressure,level control valves we are using in which type parameter side using ti,td clearly tell me
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)