what is mean by hot loop and cold loop testing, whts
different between both
Answers were Sorted based on User's Feedback
Answer / mrmk
Cold Loop checking: Checking of wires continuity of
respective field instrument-Junction box-DCS/PLC
marshalling panel terminal.
Hot loop checking: Once you powerup your field instrument
through DCS/PLC system, by stimulating process input from
respective field instrument and cross check its responce at
DCS/PLC sytsem
| Is This Answer Correct ? | 156 Yes | 6 No |
Answer / gray
Following the IEC guidelines (62382), there is no such
thing as a cold and hot loop check.
There is a wiring/ point to point that all should do before
carrying out a loop check from field device to DCS display.
| Is This Answer Correct ? | 7 Yes | 29 No |
What are different types of orifice plates? State their uses.
Draw a complete P&ID of a flow suction tank indicating all control & protection equipment. Indicate all its inlets and outlets. Explain the controls for this system
Explain the working principle of variable frequency drive?
what is orfics working in main steam line. is it increase pressure, velocity of steam flow and dicrease steam flow rate. or any other
what is air to open and air to close control valve and difference btwn this...and how to measure milli amp by this...and what is the role of positioner and i/p converter in this..plz help me
Can we used Condensate Pot on flow transmitter which is using on liquid having sluge and DP transmitter is in pit and below the process line,Can we used Condensate pot for accamulate the Sluge?
What is the formula of vabration sesore. i mean how to covert mils to volt plz share if any body knows very argent : my mai is merajalam143545@yahoo.com
With N nodes and B branches what will have a network ???
what is the use of impulse line in AFBC boiler , WHY WE CONNECT IMPULSE LINE TO TRANSMITTER , DRFT GAUGE ETC ????????
a pressure transmitter with a range of 0 to 2500kpag has a specified accuracy of 0.5 % of span.It is to be calibrated using a comparison gauge to have an accuracy of 0.1% of span.The comparison gauge has a range of 0 to 3000kpag What is the accuracy ratio? is this ratio acceptable?
what are the levels of automation?
tell how to calibrate a magnetic flow tx, vortex flow tx,dp flow tx,nozzle flow tx and venturi flow tx?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)