Answer / carl_ellis
A draft range measurement is typically a gauge pressure
measurement, referenced to atmosphere.
Draft range is very, very low pressure, so DP transmitters
are typically used because they're readily available in
a 'draft' range with the large diaphragms necessary for low
pressure measurements.
The high side is connected to the process with an impulse
tube. The low side is exposed to atmospheric pressure.
Good practice puts a filter, like a scintered pneumatics
filter on the low side, so that dirt doesn't fill the low
side cavity and air movement (wind, passing vehicles) is
buffered and damped to prevent the forces of air movement
on the low side from affecting the draft measurement.
If the impulse line were connected to the low side, the DP
would be negative, a DP subtracts the low side pressure
from the high side pressure (atmosphere minus some positive
pressure = negative pressure). Convention says that draft
range is positive so the impulse connection is to the high
side, to get a positive value.
Tell 'em Carl sent you.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / deepak
Dear Carl,
Cant we use an Absolute pressure transmitter ?
| Is This Answer Correct ? | 1 Yes | 0 No |
how to calibrate level transmitter
what is the meaning of GK value(fullform) in flowmeter ?
What is pipe schedule? What are all effects its having in the valve? how do we take care of pipe sch in case if the customer dint specify in the data sheet. What we need assume and in what basis?
What is the difference between local indicator(flow) and flow indicator?
Q- Why Phase tester is only used for checking AC not DC ?
what is difference between RTD , thermo couple and thermistor in general ?? (except temperature co-efficient )
List three types Level Switches with their working principles
plz tell me clearly about PID.."when v have to change I value,D value,GAIN??
i am going to attend ongc exam this coming june for Graduate Engineer Trainee post if anybody knows the question pattern or have experience plz share it with me
how to set calibration range in a DP transmitter to measure level for a closed tank and for an open tank,and also please explain me how to set calibration range for a DP flow transmitter in a line ?
what is the working principal of pribe
key exchanges in wpa,wpa2,tls
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)