Furnace draft transmitter range is -50 to +50 mmwc. why the
impulse line connected in hp side?
Answers were Sorted based on User's Feedback
Answer / carl_ellis
A draft range measurement is typically a gauge pressure
measurement, referenced to atmosphere.
Draft range is very, very low pressure, so DP transmitters
are typically used because they're readily available in
a 'draft' range with the large diaphragms necessary for low
pressure measurements.
The high side is connected to the process with an impulse
tube. The low side is exposed to atmospheric pressure.
Good practice puts a filter, like a scintered pneumatics
filter on the low side, so that dirt doesn't fill the low
side cavity and air movement (wind, passing vehicles) is
buffered and damped to prevent the forces of air movement
on the low side from affecting the draft measurement.
If the impulse line were connected to the low side, the DP
would be negative, a DP subtracts the low side pressure
from the high side pressure (atmosphere minus some positive
pressure = negative pressure). Convention says that draft
range is positive so the impulse connection is to the high
side, to get a positive value.
Tell 'em Carl sent you.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / deepak
Dear Carl,
Cant we use an Absolute pressure transmitter ?
| Is This Answer Correct ? | 1 Yes | 0 No |
how to draw a flowchart for swapping two numbers using bit wise operators?
why can't we use 5-20mA standard or some other instead of 4- 20mA?
where we are used split range control
if change the pid in D value so what action.
how to calibrate displacer type level transmitter by dry weight method please mention formula for weight calculation
Why Instrumentation Air Compressor called as Instrumentation Air compressor?pls dont just tell its trasferring IA to all transmitter,valves.I need exact reason, please......................
Whether the DI, DOs shields can be connected with Analog Input Shield Earthpit?
Why the tapping connections are taking above for gas service and below for liquid service?
line up procedure for dp type flow transmitter?
what is XV and KV valves?
why 1 to 5 vdc is used for output measurment
how to calibrate bubbler type level transmitter of rosemount make and how to set air flow according to the range.. give one calibration procedure with one example
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)