Furnace draft transmitter range is -50 to +50 mmwc. why the
impulse line connected in hp side?
Answers were Sorted based on User's Feedback
Answer / carl_ellis
A draft range measurement is typically a gauge pressure
measurement, referenced to atmosphere.
Draft range is very, very low pressure, so DP transmitters
are typically used because they're readily available in
a 'draft' range with the large diaphragms necessary for low
pressure measurements.
The high side is connected to the process with an impulse
tube. The low side is exposed to atmospheric pressure.
Good practice puts a filter, like a scintered pneumatics
filter on the low side, so that dirt doesn't fill the low
side cavity and air movement (wind, passing vehicles) is
buffered and damped to prevent the forces of air movement
on the low side from affecting the draft measurement.
If the impulse line were connected to the low side, the DP
would be negative, a DP subtracts the low side pressure
from the high side pressure (atmosphere minus some positive
pressure = negative pressure). Convention says that draft
range is positive so the impulse connection is to the high
side, to get a positive value.
Tell 'em Carl sent you.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / deepak
Dear Carl,
Cant we use an Absolute pressure transmitter ?
| Is This Answer Correct ? | 1 Yes | 0 No |
How can you add value to this Industry if offered the job?
for what purpose strain guage is used?
what is the PC interface and software for connection to ABB logic module “ LM011-CE18RAC “ ( for Programming ) ??
what is hall effect?where it is use in power plant?
What is the purpose of MATLAB?
1.what is beta in control valves? 2.what is the condition followed by light in LASERs? 3.1kg/cm2=?psi 4.Integral action reduces what? 5.about vena contracta 6.a simple RC circuit 7.thermistor material's temp coefficient of resistance 8.if wave passes through the thicker area of a chord to a thinner area what changes will occur to wavelength? 9.if 4-20 mA represents 0-10 kg/cm2 what will be the current when pressure is 5 kg/cm2.................
what will happen if transmitter wire get shoted?
How will you change the action of a control valve?
what is the process to make control schematic ?
How to convert 0-2500mmH2o into kg/hr? Or how to convert mmH2O into kg/hr,t/hr etc
what are different types of cables used in instrumention how to calibrate a level transmitter online ( rosemount )
What is the basic difference between 2 Wire, 3 Wire and 4 Wire RTD
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)