in 50 mw generator if field is open in full load running
condition what happen and for protection which relay used?
Answers were Sorted based on User's Feedback
Usually we are using a loss of excitation rely. Which
always getting a sense from the field excitation circuit
continueslly during the runing condition of Generator.
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / a1
I is depend on type of operation-
1) If parrallel with grid/Other generator, than it will
draw reactive power from the Grid/Generator and give active
power to the load. It will work as a Induction Generator.
Reactive power of connected circuit will unbalance.
2) If Generator is running island mode(without any other
source), than terminal voltage of genertor will start to
decrease and current will start to increase. Winding temp.
of Generator and drives will increase.
Under excitation relay provide for this.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / deepak
it run as induction gen & draw excitation power from grid
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / prodip das
It acts as a load, Sensing relay of excitation voltage
| Is This Answer Correct ? | 0 Yes | 2 No |
what is the ohmic value of transformers
what is the VA(Volt-amphere)? define with calculation?
What are the Safety measures in central chiller plant? Explain them?
22 Answers Carrier, CPIC, HSL, JLL,
xfhnchncv?
how to calculate short circuit calculation of the transformer by usuing the percentage impedence? formula needed.
our company have 750 kva oil transformer.still we have facing a problem that is when voltage is 11.5 kv coming from HT side then LT-side voltage is 420v or above at tape 1.please give me best solution to decrease the voltage.
which protection function should measure RMS value of current&DFT value of current?
What should be value of Circuit breaker operating time and tripping time?
Whether the Dc motor Droping the power factor like AC motor if lot of motor running in factory is it necessary to connect capacitor bank
i have 2 motor of same rating. on no load condition one motor take 1.6A but other motor is taking 4.8A. what is the reason of this. please explain with proof.
why ten delta testing is carried out on power transformer
what is the basic paramter to set a electric drive
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)