Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to calculate short circuit calculation of the transformer
by usuing the percentage impedence?

formula needed.

Answers were Sorted based on User's Feedback



how to calculate short circuit calculation of the transformer by usuing the percentage impedence? ..

Answer / k.prakashchandra

= Ifl x 100 / percentage Z

Is This Answer Correct ?    7 Yes 1 No

how to calculate short circuit calculation of the transformer by usuing the percentage impedence? ..

Answer / elangovan kp

Isc (Shot circuit Current ) = Full load current of Tranformer / Impedance(%)

Ex: for 1000 KVA, 11/0.415 KV Transformer , Percentage Impedance - 6% :

Full load current of LV side of Transformer = 1000 * 1000 / ( 415 * 1.732)

= (1391 / 6) * 100

= 23187 Amps.

Is This Answer Correct ?    4 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

how is reactive power controlled on the transmission system

2 Answers  


What do you mean by creepage distance?

4 Answers   Amara Raja,


we have provided 30 mA rccb to water cooler.but we feel shock in cooler body.what is the reason?

3 Answers   FCC,


1-What is the difference between absorption factor and polarization factor in insulation resistance test in transformers? and why we inject until ten minutes to get polarization factor?

1 Answers  


why single phase induction motors are not self staring ? how can we start the 1-phase Induction motor ?

3 Answers   BDL,


Energy metering: On the property I am renting, the supply voltage is 2 x 110 volts. These 2 x phases enter a energy meter which then exit the meter to over head lines to my house. Question 1. The meter is single phase 240 volts but is being used as 2 x phase(2 x 110volt), is this acceptable? if not, please give me the reasons. The meter details are as follows: 60Hz 15amp Imax 100 amp Kd 3,6 Wh/R 1 fase 3 hilos Model FX 231. I think it was manufactured in Brasil From this meter, the cables run along over head aluminum conductors,I estimate the cross sectional area to be 25mm diameter, but the neutral is only about 10mm square diameter, which cover a distance of 170 meters and then terminate with an underground cable of 65 meter length, total length = 235 meters. There must be a huge voltage drop over this length. This line is protected with 2 x 200 amp aluminum fuses after the meter, there is no main switch in the distribution board. These 2 phases connect directly onto 2 busbars. Surely the neutral should be the same size as the conductors if not more? Question2. What are your thoughts about this installation, should there be better protection, is the neutral too small? During the night, the lights dim then brighten all the time, this cannot be good for my electrical appliances. In my home, I only have a small electric geyser and fridge, my stove works off gas. But when i use other appliances like the washing machine or microwave oven, the light dim. The internal wiring of this house is done with solid hard drawn copper wires and of course, they have to be under rated. I am a retired electrician by trade, but not on the metering and over head mains side, my experience is on the factory maintenance side of things. Your expertise on these matters will be greatly appreciated. Please inform me how to rectify or make any improvements Kind regards, my power bill is very expensive, so I need to know how to bring it lower. Kind regards, Brian

1 Answers  


Why a Transformer Noise during its running condition ??

11 Answers   NTPC, UPPCL,


what is difference b/w earth and ground?

7 Answers   TATA, TCS,


how much allowable resistance that can be difference in motor all coils?

0 Answers  


WHWT IS USE OF VACCUM CIRCUIT BREAKER

4 Answers  


How to Calculate KA Rating of Main LT Panel

0 Answers  


wht factor are considered to design ACB( air Circuit reaker) 415V

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)