how to calculate short circuit calculation of the transformer
by usuing the percentage impedence?
formula needed.
Answers were Sorted based on User's Feedback
Answer / elangovan kp
Isc (Shot circuit Current ) = Full load current of Tranformer / Impedance(%)
Ex: for 1000 KVA, 11/0.415 KV Transformer , Percentage Impedance - 6% :
Full load current of LV side of Transformer = 1000 * 1000 / ( 415 * 1.732)
= (1391 / 6) * 100
= 23187 Amps.
Is This Answer Correct ? | 4 Yes | 0 No |
How will you determine the rating of a motor for continuous duty variable load motor applications?
What are the methods/types of distance protection schemes used in transmission system?
How to know the back up time for a 5KVA UPS which is connected to 15 nos. of computers? Is there any formula for this? pls. tell me.
hai now i am working as a electrical design engineer in construction field can i get a job in oil and gass field or power plant project as a electrical design engineer?
If load is 240 kw & pf is 0.8 lagging, than how to increase it from0.8 to 1.0(unit),which rating capacitor used, please give me Calculation. What is effact of consumer & suplier if pf is lagging or leading with on effect machines/ TF/GE etc.
Hi,Any one has idea regarding the KPTCL Recuirtments for AE'e & JE's for the year of 2009-10???Kindly help in regards..
wat is the difference between real power and reactive power..which is useful..?and how it s useful..wat is the effect of these on a power system...
what is phase and neutral.
what are thw types of turbines use in biogas plant?
what is the function of turbo in dg sets
What_is_mean_by_negative_dc_voltage? why we use -48v except +48v in DC power supply systems.
Why field resistance is greater than the armature resistance in dc mechine
1 Answers Cape Peninsula University of Technology,