how to calculate short circuit calculation of the transformer
by usuing the percentage impedence?
formula needed.
Answers were Sorted based on User's Feedback
Answer / elangovan kp
Isc (Shot circuit Current ) = Full load current of Tranformer / Impedance(%)
Ex: for 1000 KVA, 11/0.415 KV Transformer , Percentage Impedance - 6% :
Full load current of LV side of Transformer = 1000 * 1000 / ( 415 * 1.732)
= (1391 / 6) * 100
= 23187 Amps.
| Is This Answer Correct ? | 4 Yes | 0 No |
how is reactive power controlled on the transmission system
What do you mean by creepage distance?
we have provided 30 mA rccb to water cooler.but we feel shock in cooler body.what is the reason?
1-What is the difference between absorption factor and polarization factor in insulation resistance test in transformers? and why we inject until ten minutes to get polarization factor?
why single phase induction motors are not self staring ? how can we start the 1-phase Induction motor ?
Energy metering: On the property I am renting, the supply voltage is 2 x 110 volts. These 2 x phases enter a energy meter which then exit the meter to over head lines to my house. Question 1. The meter is single phase 240 volts but is being used as 2 x phase(2 x 110volt), is this acceptable? if not, please give me the reasons. The meter details are as follows: 60Hz 15amp Imax 100 amp Kd 3,6 Wh/R 1 fase 3 hilos Model FX 231. I think it was manufactured in Brasil From this meter, the cables run along over head aluminum conductors,I estimate the cross sectional area to be 25mm diameter, but the neutral is only about 10mm square diameter, which cover a distance of 170 meters and then terminate with an underground cable of 65 meter length, total length = 235 meters. There must be a huge voltage drop over this length. This line is protected with 2 x 200 amp aluminum fuses after the meter, there is no main switch in the distribution board. These 2 phases connect directly onto 2 busbars. Surely the neutral should be the same size as the conductors if not more? Question2. What are your thoughts about this installation, should there be better protection, is the neutral too small? During the night, the lights dim then brighten all the time, this cannot be good for my electrical appliances. In my home, I only have a small electric geyser and fridge, my stove works off gas. But when i use other appliances like the washing machine or microwave oven, the light dim. The internal wiring of this house is done with solid hard drawn copper wires and of course, they have to be under rated. I am a retired electrician by trade, but not on the metering and over head mains side, my experience is on the factory maintenance side of things. Your expertise on these matters will be greatly appreciated. Please inform me how to rectify or make any improvements Kind regards, my power bill is very expensive, so I need to know how to bring it lower. Kind regards, Brian
Why a Transformer Noise during its running condition ??
what is difference b/w earth and ground?
how much allowable resistance that can be difference in motor all coils?
WHWT IS USE OF VACCUM CIRCUIT BREAKER
How to Calculate KA Rating of Main LT Panel
wht factor are considered to design ACB( air Circuit reaker) 415V
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)