We are using 4 MVA transformer and we provided 2 separate earthing pit for Body and 2 separate earthing pit for neutral, can we connect separate body earthing pit to other earthing pit (Equipment earthing)?
Answer / riaz abbasi
No, we can not connect equipment earthing with body earthing because in case of earth fault , current will also run in the body via equipment earthing system and will damage other equipments which are installed over the Transformer.
| Is This Answer Correct ? | 3 Yes | 0 No |
What is the Temperature to be set in Thermostat provided in Marshalling box of the Transformer / Motor.
what is servo motor & how does it work.
what is the difference between ac and dc generator
As we know induction squirrel cage motor torque Directly praprortinal to applied voltage in star connection & delta also. If I connect 55KW Motor to DOL starter in load condition does motor withstand the load & what will be the current withdrawn ? motor will not fail ?
1.what is difference between line,neutral and earth 2.IF single phase voltage is 230v ac and what should be the voltage between line to neutral,neutral to earth and earth to line
what is the differance of acb and mcb and mccb
how the fan is switched off immediately switching off the switch?
What is the difference in Line PT & Bus PT.
what is meant by armature reaction?
PID controller details
The loads are connected with phase and ground then why current flow as the loads ?
how to calculate the earth fault current
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)