Why Transformer in KVA?
Answers were Sorted based on User's Feedback
Answer / raja
bcz....transformer does nt depens upon the power factor
that y ratings r in kva
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / r.emanuel james
Rating of the equipment connected to T/F depends upon the
power factor since the load power factor to which
T/F is supplying power is not known , it may be any type
of load (capacitive ,resistive , or inductive) that is why
its rating is mentioned in KVA
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / arvind singh
kVA is the unit for apparent power. Apparent power consists
of active and reactive power. Active power is the share of
the apparent power which transmits energy from the source
(generator) to the user. Reactive power is the share of the
apparent power which represents a useless oscillation of
energy from the source to the user and back again. It
occurs when on account of some »inertia« in the system
there is a phase shift between voltage and current. This
means that the current does not change polarity synchronous
with the voltage. But the heat generated in a winding as
well as the eddy current losses generated in a transformer
core depend on the current only, regardless of whether it
aligns with the voltage or not. Therefore the heat is
always proportional to the square of the current amplitude,
irrespective of the phase angle (the shift between voltage
and current). So a transformer has to be rated (and
selected) by apparent power.
| Is This Answer Correct ? | 2 Yes | 0 No |
Transformer manufacturers design transformers on the basis
of no. of turns such that primary NI = secondary NI. Also
primary VI = secondary VI. The manufacturers design
transformers for Maximum (constant for every transformer)
power. As we know
KW = KVA x power factor
So for unit power factor
KW = KVA
and if load is inductive/capacitive then
KW < KVA
Manufacturers do not know whether transformer would be used
for inductive/capacitive/resistive load.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / vipul rajput
1) X'mer is static device.
2)Power factor is not consider in case of transformer..so
its rating depend only on current & voltege.
P=V.A (p.f. is not consider)
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / jugal
As rating unit of any equipment depend upon the factora
which influence its output,and output depend upon the
losses. so as in transformer the cupper loss depend upon
current and iroin loss depend upon the vlotage,and not on
powerfactor.
as we know kw= volt*current8power factor
and Kva= vlot*amp
so its very logical; to rate the transformer in KVA
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / akash pandey
if a transformer is of X VA then it means that this is the
burden of secondary side and also we knoe that this output
power is limited by the losses namely the core loss
depending on V and ohmic losses depending on I hence the
rating is given in VA. Consider a case where the power
factor of the load is ZERO hence the power delivered will be
zero but losses will still be there ...hence the output
varying with the condition ...but whats constant is VA.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / yogesh kumar
kVA is the unit for apparent power. Apparent power consists
of active and reactive power. Active power is the share of
the apparent power which transmits energy from the source
(generator) to the user.
Reactive power is the share of the apparent power which
represents a useless oscillation of energy from the source
to the user and back again.
It occurs when on account of some »inertia« in the system
there is a phase shift between voltage and current. This
means that the current does not change polarity synchronous
with the voltage. But the heat generated in a winding as
well as the eddy current losses generated in a transformer
core depend on the current only, regardless of whether it
aligns with the voltage or not. Therefore the heat is
always proportional to the square of the current amplitude,
irrespective of the phase angle (the shift between voltage
and current). So a transformer has to be rated (and
selected) by apparent power.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / omnarayan tiwari
kVA is the unit for apparent power. Apparent power consists
of active and reactive power. Active power is the share of
the apparent power which transmits energy from the source
(generator) to the user. Reactive power is the share of the
apparent power which represents a useless oscillation of
energy from the source to the user and back again. It
occurs when on account of some inertia in the system there
is a phase shift between voltage and current. This means
that the current does not change polarity synchronous with
the voltage. But the heat generated in a winding as well as
the eddy current losses generated in a transformer core
depend on the current only regardless of whether it aligns
with the voltage or not. Therefore the heat is always
proportional to the square of the current amplitude
irrespective of the phase angle (the shift between voltage
and current). So a transformer has to be rated (and
selected) by apparent power.
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / joy das gupta
In X-former two losses- Cu loss and Iron loss.Hence Cu loss
depends on Current(A) and Iron loss depends on
Voltage(v).There is no phase angle between them. Again in
the output side of the X-former, we don't know the types of
load(Inductive , Capacitive, Resistive) which is connected
with secondary coil. Though it is not, we cant fixed the
power factor and it can vary. So under consideration of
losses and avoid the load pf variety, the transformer rating
given in KVA.
| Is This Answer Correct ? | 0 Yes | 0 No |
one cable insulation resistance 200 mega ohm. how find 250 meter cable resistance.
Define over current & earth fault ?how its functioning ?
During a temperature rise test of a bus duct, it is fed with 415 volts at 2000 amperes. Why dont we get an electric shock if we touch the bus bars?
Dear all, I just want to ask an expert on this forum for some insights. For the magnetic balance test, when applied voltage on a Delta-Star transformer e.g. Dyn11, the following relationships apply for HV side: 1. H1-H2 = H2-H3 H3-H1 2. H2-H3 = H3-H1 H1-H2 3. H3-H1 = H1-H2 H2-H3 For the LV side also: 4. X1-X0 = X2-X0 X3-X0 5. X2-X0 = X3-X0 X1-X0 6. X3-X0 = X1-X0 X2-X0 Is there a similar pattern for Y-d, Y-Y, D-d? And how about Y-z, D-z, Z-y transformers? I've tested a YNzn5 transformer and for LV side I don't see the pattern. In this particular case I got for LV side the following (see values below): H1-H0 H2-H0 H3-H0 X0-X1 X0-X2 X0-X3 128.0 119.9 7.2 29.2 13.3 15.8 70.7 128.4 59.2 23.4 22.0 3.6 7.2 120.1 128.1 13.4 29.3 15.8 What is the relationship here for LV? For row 1 I see the relationship, for row 3 I also see but it's shifted, but for row 2 I don't see such relationship. Any suggestions, answers, someone?
hi can anyone pls tell me the eee interview core questions asked in l&t
what is V0/V rating of cable
What type of bulb used in small size cross symbol boder and original flame type(Deepam)?
Connection diagram for KW meter and Kva meter
can we use ACB for HT supply
what is the use of earthing ?
If you touch at the end welding machine, will you have shock ?
what is the different between rms and average value
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)