if we convert Ampers into kva,which one formula use by
us,pls tell me?

Answers were Sorted based on User's Feedback



if we convert Ampers into kva,which one formula use by us,pls tell me?..

Answer / jaykaran gadhvi

the answer is


line current =kva( 3 phase) / (sqrt(3)* line voltage in kv)

so

kva ( 3 phase) = sqrt(3)* line voltage in kv * ampere

Is This Answer Correct ?    15 Yes 0 No

if we convert Ampers into kva,which one formula use by us,pls tell me?..

Answer / joseph

You can use the basic formula:

VA = [Voltage X 1.732] * Current
or
VA = [Voltage * 1.732] * I

Hence, VA of a 3 Phase system with 1500A Current current at
440V will be:

VA = [440 * 1.732] * 1500
= 1143120 VA or 1143 KVA.

Is This Answer Correct ?    12 Yes 2 No

if we convert Ampers into kva,which one formula use by us,pls tell me?..

Answer / ssnslm

KVA = KV * A

Is This Answer Correct ?    11 Yes 7 No

if we convert Ampers into kva,which one formula use by us,pls tell me?..

Answer / v.chandrasekharreddy

Amps when
kVA is known ,I=KVA*1000/[1.732*VOLTAGE]IN THREE PHASE

Amps when
kVA is known
I=kVA x 1000/VOLTAGE SINGLE PHASE

Is This Answer Correct ?    10 Yes 6 No

if we convert Ampers into kva,which one formula use by us,pls tell me?..

Answer / n.vijayakumar

the formula is

kva=a*1.732*v/1000

Is This Answer Correct ?    2 Yes 1 No

if we convert Ampers into kva,which one formula use by us,pls tell me?..

Answer / yogesh raste

In order to convert amperes to KVA multiply supply voltage
(V) with current(I).

Is This Answer Correct ?    0 Yes 0 No

if we convert Ampers into kva,which one formula use by us,pls tell me?..

Answer / p.baskar

Amps =KVA*1000/[1.732*VOLTAGE]IN THREE PHASE

Amps =kVA x 1000/VOLTAGE SINGLE PHASE

Is This Answer Correct ?    0 Yes 0 No

if we convert Ampers into kva,which one formula use by us,pls tell me?..

Answer / thebalu007

kw = Route that mean 1.732*v*i*cosPai

I = route that mean 1.732*V

because kva does not having power factor that men cos pai

Is This Answer Correct ?    0 Yes 0 No

if we convert Ampers into kva,which one formula use by us,pls tell me?..

Answer / dinesh jakhar

Apparent power =V.A

Unit of apparent power is VA or KVA or MVA

So if you want to find KVA simple formula u just need voltage and current

kVA= KV(voltage) * A (current)

Is This Answer Correct ?    0 Yes 0 No

if we convert Ampers into kva,which one formula use by us,pls tell me?..

Answer / subhash chand

1kva ( 3 phase ) = 1.39 Ampere

Is This Answer Correct ?    2 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

what is the safe meggar values for motor, transformer HT, LT and Cables? IF we want to replace I/C bay at our 220 kv substation which is of 140 mw load capacity bay to be replaced by 400 mw capacity bay.other than CT(1200/1) what are the other equipment i have to replace. why we generally use 3.5 core cable or in other word 1/2 core for neutral and also confirm me that in balance conditiob(3 phase)current in neutral will zero

0 Answers   Jindal,


what is the principle of the single phase energy meter? and,what is the advantages and disadvantages of single phase energy meter?

0 Answers  


Do any one know exacatly when the results for NHPC held on 8th march 09 for engineering trainees will be released ?. if so please post it, i'm eager to know it.

0 Answers   NHPC,


The potential difference between a phase and neutral is 230v , but the potential difference between two phases is 400v. why?

4 Answers   HCL,


How do you reset circuit breaker?

1 Answers   Bhel, Kaveri Steels,






what is the calculation method to design core and winding of a 200kva 3phase distribution transformer?

0 Answers  


What is the formulae of Megger value for a A.C.Motor

0 Answers  


How does a digital electronic meter work??????

0 Answers  


Hello sir i m student of gtu .what is idp.

0 Answers  


What do you mean by PT-100?

8 Answers  


how to select cable size according to ampere.

1 Answers  


As we know induction squirrel cage motor torque Directly praprortinal to applied voltage in star connection & delta also. If I connect 55KW Motor to DOL starter in load condition does motor withstand the load & what will be the current withdrawn ? motor will not fail ?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)