if we convert Ampers into kva,which one formula use by
us,pls tell me?
Answers were Sorted based on User's Feedback
Answer / jaykaran gadhvi
the answer is
line current =kva( 3 phase) / (sqrt(3)* line voltage in kv)
so
kva ( 3 phase) = sqrt(3)* line voltage in kv * ampere
| Is This Answer Correct ? | 15 Yes | 0 No |
Answer / joseph
You can use the basic formula:
VA = [Voltage X 1.732] * Current
or
VA = [Voltage * 1.732] * I
Hence, VA of a 3 Phase system with 1500A Current current at
440V will be:
VA = [440 * 1.732] * 1500
= 1143120 VA or 1143 KVA.
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / v.chandrasekharreddy
Amps when
kVA is known ,I=KVA*1000/[1.732*VOLTAGE]IN THREE PHASE
Amps when
kVA is known
I=kVA x 1000/VOLTAGE SINGLE PHASE
| Is This Answer Correct ? | 10 Yes | 6 No |
Answer / yogesh raste
In order to convert amperes to KVA multiply supply voltage
(V) with current(I).
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / p.baskar
Amps =KVA*1000/[1.732*VOLTAGE]IN THREE PHASE
Amps =kVA x 1000/VOLTAGE SINGLE PHASE
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / thebalu007
kw = Route that mean 1.732*v*i*cosPai
I = route that mean 1.732*V
because kva does not having power factor that men cos pai
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / dinesh jakhar
Apparent power =V.A
Unit of apparent power is VA or KVA or MVA
So if you want to find KVA simple formula u just need voltage and current
kVA= KV(voltage) * A (current)
| Is This Answer Correct ? | 0 Yes | 0 No |
DIFFERANCE BETWEEN function of ELCB? function of rccb? function of mccb? function of acb? function of mcb?
What is essential to prove safe isolation of electrical circuit?
why we use end termination xlpe cable on ht kit
What the difference between ac and dc inductor an capacitor
HOW TO FIND OUT 1. LINE CURRENT, 2. PHASE CURRENT IN AN ALTERNATOR / TRANSFORMER WHICH IS FEEDING A I)STAR LOAD ii) DELTA LOAD, USING A CLAMP METER. NORMALLY WHEN WE USE CLAMP METER IN A DG SET THEN WHAT DO WE GET?? PHASE CURRENT OR LINE CURRENT.
Sir we have 12.5 MVA(110/11KV) transformer (Y-Y) connected,which tripped showing earth fault,when we charged transformer it stood OK ,but on connecting 11 KV feeders it tripped showing earth fault.our service engineers found that the B phase and R phase phase connecting to neutral broken from HV OLTC(on load tap changer),and R phase and Neutral is ok.Dissolved gas analysis shows that accetline content is high,tan delta value is 12.My dout is it is an internal fault of transformer,why REF or diffrential relay is not acted?
how to calculate the output power of vfd , please help me.
difine electrical ballast in HPSVL
why we used servo motor insted of inducation motor?
DOES AN EARTH FAULT CURRENT ON THE DELTA SIDE OF A 6.6/33KV STEP UP STAR-DELTA CONNECTED TRANSFORMER REFLECT ON THE STAR SIDE? IF YES, THEN HOW AND WHAT IS THE AMOUNT OF CURRENT REFLECTED?
what is the concept of directional power?
Ammeter of 1 ohm resistance measure max 10 ohm to measure higher resistance from it
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)