Why Transformer in KVA?
Answers were Sorted based on User's Feedback
Answer / nikunj
As we know Cu loss depends on current & iron loss depends
on voltage and not affected by power fector hence always
transformer ratting defined in KVA not in Kw.
Is This Answer Correct ? | 315 Yes | 31 No |
Answer / manoj kumar
actually rating of the machine (kva or kw) depends upon the
power factor since the load power factor to which
transformer is supplying power is not known , it may be
capacitive ,inductive , or resistive that is why its rating
is in kva and not in kw
Is This Answer Correct ? | 260 Yes | 94 No |
Answer / padmanaban
Since Transformer is a Static device and it is having two
losses namely core loss and Cu loss. The core loss depends
on the Voltage (V) only, where Cu loss depends on Current
(I) only.So for this purpose the transformer always called
its rating in apparent power only(VA).
Is This Answer Correct ? | 166 Yes | 25 No |
Answer / saravana babu
bcoz ..cu loss depends the current.iron loss depends the
voltage..so that total loss of transformer is depends
voltage,current...so the transformer ratings in KVA..
Is This Answer Correct ? | 59 Yes | 15 No |
Answer / niranjan
Transformer is a static device having two type of losses
such as ironlossed and cupper losess. since iron losses
depends upon voltage(V) and cupper lossed depends upon on
the curret(I) so rating of Transformer is in KVA
Is This Answer Correct ? | 32 Yes | 8 No |
Answer / pankaj rajput
The leading/lagging power factor has
magnetizing/demagnetizing effect on armature reaction in a
rotating electrical machine. Hence the losses depends on
the load power factor. Unity PF has neither magnetizing nor
de-magnetizing effect.
Whereas in a transformer, the power factor doesn't play any
role in machine losses i.e. Cu & core losses are
independent of power factor.
Hence the rating of transformer is always given in KVA and
the rating of generators is given in kW at certain pf i.e.
usually at 0.8 lag.
Is This Answer Correct ? | 31 Yes | 13 No |
Answer / krishnendran
kVA is the unit for apparent power. Apparent power consists
of active and reactive power. Active power is the share of
the apparent power which transmits energy from the source
(generator) to the user. Reactive power is the share of the
apparent power which represents a useless oscillation of
energy from the source to the user and back again. It
occurs when on account of some »inertia« in the system
there is a phase shift between voltage and current. This
means that the current does not change polarity synchronous
with the voltage. But the heat generated in a winding as
well as the eddy current losses generated in a transformer
core depend on the current only, regardless of whether it
aligns with the voltage or not. Therefore the heat is
always proportional to the square of the current amplitude,
irrespective of the phase angle (the shift between voltage
and current). So a transformer has to be rated (and
selected) by apparent power.
Is This Answer Correct ? | 21 Yes | 3 No |
Answer / pankaj rajput
The copper loss of a Transformer depends on current i.e.
I^2 R and the iron loss depends on voltage. Hence the total
losses depends on volt-ampere (VA) and not on phase angle
between voltage & current.
Therefor the losses in a transformer are independent of
power factor which is cosine of angle between voltage &
current.
That's why the rating of transformers is in KVA and not in
kW.
Now coming to Efficiency of a transformer: Yes it depends
on power factor of load. Because the
Efficiency = Output/Input
= (Input - Losses) / Input
= 1 - (Losses / Input)
= 1 - [Losses / (Vs * Is * Cos phi + Losses)]
Efficiency is inverted V curve (Y-scale) and the peak of
curve appears between 50-60% load (X-scale)for various load
power factors. Efficiency increases as the power factor
increases.
Is This Answer Correct ? | 23 Yes | 6 No |
Answer / vidushi
The X-mer o/p is limited by heating and hence by the losses
in the X-mer. There are two kinds of losses in the X-mer:
copper losses (ohmic losses) and iron losses. ohmic losses
(I*I*R) depend upon current while core losses depend upon X-
mer voltage and are almost unaffected by X-mer P.F.. Hence
the rated o/p is expressed in VA (V*I) or in KVA and not in
KW.
Is This Answer Correct ? | 14 Yes | 3 No |
Answer / kapil bahadure
Transformer is the statics device.actually rating of the
machine (kva or kw) depends upon the power factor since the
load power factor to which transformer is supplying power
is not known , it may be capacitive ,inductive , or
resistive that is why its rating is in kva and not in kw.
P=VIcosø
cosø is the depen upon the load & load not cosider the
manufacturing compony of transformer.then only VI
consider.so its rating is in kva.
Is This Answer Correct ? | 13 Yes | 4 No |
What is the meaning of ST and HT in electrical transmission and what are thier range.
My load is 15 kw,i want to improve power factor from 0.8 to 0.9,how select capacitor
if we connect a ohmmeter across shorted capacitor .what will be the reading..will it be zero or infinity
Which types of Gases occure when mineral oil burnt
what is the iron loss in a 11KV/440V transformer?
what are the industrail measures to over ferranti effect? how would the ferranti effect the power system if those remedial mearsure arent taken? how often does this effect occurs in real power system?
If I want to use capacitor banks at HT (11 KV) side for maintaining power factor then which type of capacitor should I use? Plz give me the specification?? (I am using 1250 Kva transformer (11 KV/433V)).
how the 12 pulse rectifier is made?
8 Answers Engineers India Limited,
what is the harmonics.
How do u term the word 'OF' in Megger Testing???
How can we calculate earth mat conductor size ..? & give the formula to determine earth conductor size?
what is difference between 9kv 5ka surge arrester and 9kv 10ka surge arrester.