Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How do you commission a power Transformer?



How do you commission a power Transformer?..

Answer / vishwa theja c

Commissioning Of Transformer
After finalization of the erection work the following tests
should be conducted:

Pre Test Inspection

Sample of oil taken from the transformer and subjected
to electric test (break down value) of 50KV (RMS) as
specified in IS: 335.
Release trapped air through air release plugs and valve
fitted for the purpose on various fittings like radiators,
bushing caps, tank cover, Bushing turrets etc.
The float lever of the magnetic oil level indicator (if
provided) should be moved up and down between the end
position to check that the mechanism does not stick at any
point. If the indicator has signaling contact they should be
checked at the same time for correct operation. Checking the
gauge by draining oil is a more positive test.
Check whether gas operated (if provided) is mounted at
angle by placing a spirit level on the top of the relay.
Check whether the conservator is filled upto the filling oil
level marked on plain oil gauge side and corresponding to
the pointer reading in MOG side. Check the operation of the
alarm and trip contacts of the relay independently by
injecting air through the top cocks using a dry air bottle.
The air should be released after the tests. Make sure that
transformer oil runs through pert cock of buchholz relay.
Check alarm and trip contacts of WTIs, dial type
thermometer, magnetic oil gauge etc. (if provided).
Ensure that off circuit switch handle is locked at the
desired tap position with padlock.
Make sure that all valves except drain, filter and
sampling valves are opened (Such as radiator valves, valves
on the buchholz relay pipe line if provided).
Check the condition of silicagel in the breather to
ensure that it is active and colour is blue. Also check that
the transformer oil is filled in the silicagel breather upto
the level indicated.
Check tightness of external electrical connections to
bushings.
Give a physical check on all bushing for any crack or
any breakage of porcelain. Bushing with cracks or any other
defects should be immediately replaced.
Check the neutral earthing if specified. Make sure that
neutrals of HV I LV are effectively earthed.
Tank should be effectively earthed at two points.
Check that the thermometer pockets on tank cover are
filled with oil.
If the oil temperature indicator is not working
satisfactorily, loosen and remove the thermometer bulb from
the pocket on the cover and place it with a standard.

Is This Answer Correct ?    4 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

directional over current relay when acted & how it works

3 Answers   NCC, ThyssenKrupp,


my question is Megger of cable insulation or swgr board meggerring some values in one day 50mohms,some other day checking different values(20Mohms). this tell that some person tell that that values ok. how to identify the megger value is correct. pls tell me the answer.

2 Answers  


how work the differential protection relay in details?

2 Answers  


Why HT motor is connected in Star?

3 Answers   Equate,


which motor is used in electric train...???????

27 Answers   ESPL, IOCL,


How to calculate Earth busbar size & what is the procedure we make for determine that?

1 Answers  


why the three phase transformer's star point does not sparks or seperated? while we often see that two phases touches each other it sparks and ocationaly conductor breakes out.

4 Answers  


Why the ceiling fan rotate in anticlock wise direction whereas tables fan rotates at clock wise direction?

3 Answers  


Difference between Lugs and Thimbles

0 Answers   ABB,


How to calculate the multiplying factor for energy meter with ct ratio given

0 Answers  


What is cogging and crawling phenomenon in motor.

2 Answers   DAE,


How to calculate the fuse rating depend upon the DC circuit?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)