how to select a circuit breaker?
Answers were Sorted based on User's Feedback
Answer / nilesh kumar singh
Selection of Circuit breaker
CURRENT RATING:
Transformer Rating (X)kVA
%age impedance of transformer - Z%
I Full load = X*1000/Sq. root 3*VL
Where X = Transformer rating in kVA
VL = Line Voltage
BREAKING CAPACITY:
Breaking Capacity of the breaker> I Fault Current
Fault Current (Level) = 1.1*VL/Sq. root 3*Z
Where Z = Impedance of Transformer
VL = Line Voltage
Z= %Z*10*(kV)*(kV)/KVA
MAKING CAPACITY:
Making Capacity depends upon the following:
a) Power Factor
b) Instant of switching ratio 'n' between required rate s/c
making capacity and rated s/c breaking capacity.
| Is This Answer Correct ? | 66 Yes | 12 No |
Answer / kapil
this depends on the application type where you are using
this circuit breaker. actually we will have to know whether
we require some delay in tripping after the overcurrent or a
frequent operation is needed. if a delay is needed and we
will have to bear some over temperature conditions then we
use thermal relay which has some delay and low trip current
at high temp. when we require the frequent operation then we
use magnetic type relay. also we will have to mind the
operating environment, nominal current rating and max peak
current bearing capacity and delay time of the circuit breaker.
| Is This Answer Correct ? | 71 Yes | 25 No |
CB is selected on the basis of it's Breaking capacity,
Making capacity, operating voltage, operating
current,system frequency, insulation level & type of use
i.e indoor or outdoor.
| Is This Answer Correct ? | 24 Yes | 8 No |
Answer / mahesh.s
Selection of circuit breaker mainly depends on the voltage
capacity for which its is connected in the circuit like
3.3kv,6.6kv,11kv,33kv,...etc and the breaking capacity of
that breaker means at wht current it will trip the ckt...
and making capacity,
Thermal capacity,
application like indoor or outdoor usage.
| Is This Answer Correct ? | 32 Yes | 19 No |
Answer / ammar
we have to calculate the rated current of the load
connected to the circuit breaker from the power equation
p=√3.V.I.cosθ
then we can decide which is the suitable rating for the CB.
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / gurbir singh
a ciruit breaker depend upon the total capacity of load
| Is This Answer Correct ? | 12 Yes | 6 No |
Answer / magesh
We use circuit breaker for short circuit and overload
protection
For OL -2.5 times of the rated I
For Short circuit-12times of I
According to this calculations breakers are selected
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / andy
people you all are crazy, can you answer simple question
and give simple example ?
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / rk
Rateed voltage
Normal current
breaking curren i.e. fault current fault mva
aux supply volatge
C-O-c seq for auto recl function
| Is This Answer Correct ? | 9 Yes | 7 No |
Answer / majid amoudi
direct technical answer:-
suppose if d interviewver asks u
"for 11kva transformer what size of d ckt breaker shud b used"
answer-
11kva= 11,000va
11,000 divided by 220v(depending on various countries voltage rating)=50A
50A is d current passing thru d ckt...according to NEC(national electrical code) current shud be 125%...
so, 50* 1.25=62.5A
d breaker will trip if d current passes more dan 62.5A & d ckt breaker size shud be selected 4 times d nominal ckt breaker current i.e 62.5*4=250A.
so..a MCCB(moulded case circuit breaker) of 250A shud be used for 11kva T/F.
| Is This Answer Correct ? | 2 Yes | 1 No |
How we can test the Smoke Detectors????
What will happen if i replace a inductive proximity switch with photo sensor in a machine?
what will hapen if secodery circuit is open of current transformer
whats the advantage and disadvantage in TUMETIC mdel transformer
What are the advantages and disadvantages of the ac motors?
what happens if i connect acapacitor to a generator load
(1)WHAT HAPPENS WHEN SUDDENLY LOAD GIVEN TO THE INDUCTION MOTOR ? (2)CAN WE MAKE WOOD AS MAGNET ? (3)WHAT IS THE VALUE OF MAGNETIC FLUX DENSITY IN TRANSFORMER ? (4)WHY WE ARE USING ELECTROMAGNETI NOT ELECTROSTATIC IN MACHINE ?
why there is a high voltage line in multiplication of 11?i.e.- -66kv,11,kv,22kv
Sir We have a REF relay connected to 10MVA(Y-Y) Transformer.on External earth fault REF relay trips along with earth fault relay.The REF relay has no complant as we tested relay.Why is it happening?
Types of test in Switchgears, MCC, NGR and DB's how it should be procced. Can anyone give me the details here or email me to pasuvaraj.k@gmail.com
For a Potential Transformer(PT), the primary neutral terminal must be grounded before energization. Why....? What will be heppend if we energize the PT without grounded the primary neutral point? Why..........?
what is difference between Motorised MCCB & ordinary MCCB?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)