Answer / nilesh kumar singh
Selection of Circuit breaker
CURRENT RATING:
Transformer Rating (X)kVA
%age impedance of transformer - Z%
I Full load = X*1000/Sq. root 3*VL
Where X = Transformer rating in kVA
VL = Line Voltage
BREAKING CAPACITY:
Breaking Capacity of the breaker> I Fault Current
Fault Current (Level) = 1.1*VL/Sq. root 3*Z
Where Z = Impedance of Transformer
VL = Line Voltage
Z= %Z*10*(kV)*(kV)/KVA
MAKING CAPACITY:
Making Capacity depends upon the following:
a) Power Factor
b) Instant of switching ratio 'n' between required rate s/c
making capacity and rated s/c breaking capacity.
| Is This Answer Correct ? | 66 Yes | 12 No |
Answer / kapil
this depends on the application type where you are using
this circuit breaker. actually we will have to know whether
we require some delay in tripping after the overcurrent or a
frequent operation is needed. if a delay is needed and we
will have to bear some over temperature conditions then we
use thermal relay which has some delay and low trip current
at high temp. when we require the frequent operation then we
use magnetic type relay. also we will have to mind the
operating environment, nominal current rating and max peak
current bearing capacity and delay time of the circuit breaker.
| Is This Answer Correct ? | 71 Yes | 25 No |
CB is selected on the basis of it's Breaking capacity,
Making capacity, operating voltage, operating
current,system frequency, insulation level & type of use
i.e indoor or outdoor.
| Is This Answer Correct ? | 24 Yes | 8 No |
Answer / mahesh.s
Selection of circuit breaker mainly depends on the voltage
capacity for which its is connected in the circuit like
3.3kv,6.6kv,11kv,33kv,...etc and the breaking capacity of
that breaker means at wht current it will trip the ckt...
and making capacity,
Thermal capacity,
application like indoor or outdoor usage.
| Is This Answer Correct ? | 32 Yes | 19 No |
Answer / ammar
we have to calculate the rated current of the load
connected to the circuit breaker from the power equation
p=√3.V.I.cosθ
then we can decide which is the suitable rating for the CB.
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / gurbir singh
a ciruit breaker depend upon the total capacity of load
| Is This Answer Correct ? | 12 Yes | 6 No |
Answer / magesh
We use circuit breaker for short circuit and overload
protection
For OL -2.5 times of the rated I
For Short circuit-12times of I
According to this calculations breakers are selected
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / andy
people you all are crazy, can you answer simple question
and give simple example ?
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / rk
Rateed voltage
Normal current
breaking curren i.e. fault current fault mva
aux supply volatge
C-O-c seq for auto recl function
| Is This Answer Correct ? | 9 Yes | 7 No |
Answer / majid amoudi
direct technical answer:-
suppose if d interviewver asks u
"for 11kva transformer what size of d ckt breaker shud b used"
answer-
11kva= 11,000va
11,000 divided by 220v(depending on various countries voltage rating)=50A
50A is d current passing thru d ckt...according to NEC(national electrical code) current shud be 125%...
so, 50* 1.25=62.5A
d breaker will trip if d current passes more dan 62.5A & d ckt breaker size shud be selected 4 times d nominal ckt breaker current i.e 62.5*4=250A.
so..a MCCB(moulded case circuit breaker) of 250A shud be used for 11kva T/F.
| Is This Answer Correct ? | 2 Yes | 1 No |
i am using auto transformer for starting of induction motor to provide reduse voltages...but the principle of a tansformer according to definition"which transform energy to on circuit to another circuit with constant power and constant frequency". so if i am using reduse voltage then current obsely hige because power is same.but we use auto transfarmer for starting of induction motor to give low current.but here according to definition we are giving hige current.
why overcurrent fault occurs in power system.
How do determine the Size of a Droop Current Transfomer for Paralleling of Two Generators, Say I need a Droop Current transformer for a 600 kW generator need to be parallel with a 800 kW generator, etc.
2 Answers JK Cement, MPPGCL Madhya Pradesh Power Generating Company Ltd, PNG Power,
Is it necessary to place tap changer in secondary winding or we can use on both sides?
why scott connection is done why not two phases are directly picked at the output of 3 phase transformer??
Dear sir, iam completed iti ncvt electrician 2000-2002 & diploma electrical eng completed 2008-2010 distance education in rvd university, still i got B licences only but my working company want C licences, how to i get c licencese pls reply me iam in critical situation thank you karthick 9841637803
what is the formula to calculate the fuel consumption of a diesel generator at different diferent load.
4 Answers Aegis, Network Clothing Company,
State kirchoff current law?
i am having a 3 phase 12.5HP motor,that is connected in Star/delta.Without any Trip that motor stopped suddenly why?
magnetizer priciple
As per IS why should the control be taken only from R phase, why not from B or Y phase??!!
What is the difference between Earth Fault protection & Neutral Protection
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)