Hello friends., my question is related to testing of current
transformer... A Ct having knee point voltage of 750 volts.,
and I have two step up transformer's of rating 230 v to
440 volts., can I obtain the value of 750 volts by using the
two transformer's.... If yes then how could I connect the
transformer's to obtain knee point voltage?? thank you in
advance
Answer / k.prakashchandra
Connect 230 V sides of trs in parallel with
dimmer-stat.Connect secondaries in series . Connections
should be done in such a way that the secondary voltages add
to each other.This can be ensured by measuring voltage .
Is This Answer Correct ? | 1 Yes | 4 No |
sir i completed apprentice in TNEB.apprentice is eligible for 'c' licence
0 Answers Bhel, TNEB Tamil Nadu Electricity Board,
temp of cast resin 1500kva tx formerwent up to 138.c but came down very fast to about 100.c within 20 mins when load was reduced from 70% to 60%
Assuming that a dedicated neutral earthing transformer is provided for each GT generator, when the two generators are running in parallel, has consideration been given that the earth fault current from one generator stator winding be split between the two neutral earthing transformers? If so, what adverse impact will this have on the operation of the 59N and 27TN devices?
How to choose the vector group for the step up and step down transformers??? Tell me the which vector group is suitable for step up and step down transformers and whats the reason to choose and whats the benefits???
what is cathodic protection and why it use in industries?
which protection function should measure RMS value of current&DFT value of current?
What is the functaion of IGBT in UPS system?
1. If we apply dc supply to the primary winding of transformer it will be burnt out. similarly dc supply is given to field winding of syn. motor and armature winding of dc motor, they are safe. (Remember both windings inductive nature) what is the reason behind that?
how to reduce earth resistance in sandy soil.
RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV BUT WE KNOW THAT LIGHTENING ARRESTER IS USED FOR OVER VOLTAGE PROTECTION SO WHY NOT THE RATING OF LIGHTENING ARRESTER BE MORE THAN 11KV ???????????????//
can any one provide me a connection wiring diagram for a DG set control panel along with BOM?
How to find out kvar from any particular load capacity give a formula