Answer / a.lingadurai
The winding resistace varies according to the connection
of star / delta. When star connected motor, measured
resistance shows the value of two resitance in series.
When delta connected motor,measured resistance shows the
value of two resistance series and another resistace
parallel with them. So we can identify by the value of
resitance.
Also the phase current of motor is equal to line current
for star connected motor. For delta connected motor the
line current is 1.732 times of phase current.
| Is This Answer Correct ? | 25 Yes | 4 No |
Answer / karl
Most nameplates wont say whether to connect in Delta or
Star but will show a Delta symbol or star symbol with a
voltage rating of current rating next to them. Sometimes a
symbol not even shown but 2 levels or voltage and currents.
This is because this gives you 2 choices of voltages to
connect to. Example if you have a 415V three phase supply
and your motor nameplate shows 230V Delta and 400V Star you
should connect the motor in Star. If it just shows 400V
this usually means you connect it in Delta. If you
connected this motor in Star it would not give you full
output power. These motors sometimes use a star, delta
starter which when in star runs at lower start current.
| Is This Answer Correct ? | 16 Yes | 3 No |
Answer / pillay
I agree with only KARL.If the connection is not mentioned in
the name plate than it is anybodies guess wish you best of luck.
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / naganath jamadar
All 3 phase motor are winding with RYB 3 saperate coils winding started point and finished point so totale six connection you can do it easy star or delta using links in terminal s
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shri..
As per my knowledge in star connections only three leads
are coming at terminal box.
And in star delta winding six leads are coming in terminal
box.
In star connection DOL starter are using.
In star delta starters
When pressing on button of starter the starter make star
connection after releasing the button starter makes delta
connection.
| Is This Answer Correct ? | 21 Yes | 25 No |
what is the method to measure the transformer current carrieng capacity in three phase.
The inexpensive way to improving energy efficiency of a motor which operates consistently at below 40% of rated capacity is by _____.
what is the relation between reactive power and power factor for the what is the limit of reactive power and power factor
what happen as when voltage drop(or may decrease) ? in case of atomic base theory?
How to decide the input and output circuit breaker for a 1600kva transformer.Is there any calculation is involved.
I have a 600VA numeriv digital UPS for computer only. It holds for 15 minutes only. but i am try to using home CFL Light I cant using UPS 2 or 3 secound automatic off .but computer ok how to change this is in to ups ?
why the rating of dc generator is in kw where as rating of alternator is in kva?
how much GROUND & NEUTRAL VOLT maintain in data center.
why receiving end voltage increases in a system when capacitive load is added
protection used for alternator , feeder , transmission line
What is the latest generation of circuit breakers called?
3 Answers Epitome, Focus Energy, Jakson, KDC, L&T,
lenz law application and define
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)