One Township having 850 house and each house load is 2.2KW
single phase & 5HP 3 Phase motors of 10 Nos .Who can
calculate 11 KV transformer
capacity .dilip_bhasker@yahoo.co.in
Answer / naresh
The total lighting load of the township is 1870KW and motor
load is 50HP.
We have to load the transformer upto 80percent of
its KVA rating. Because the average power factor has been
taken as 0.8 and to avoid the over loading problem.
So for the township the transformer capacity is as follows.
24x100KVA + 1x63KVA or 15x160KVA + 1x63KVA
Multiple transformers provided instead of few high
capacity transformers to avoid low voltage problem at tail
end.
| Is This Answer Correct ? | 2 Yes | 3 No |
Can I use measuring current transformers in protection purposes?
what is rated current and operating current?
Distinguish between neutral earthing and equipment earthing?
What is IGBT?Where it is used? What is the difference between IGBT and Thyristor?
5 Answers AC, Formo Plastic, HBL Power Systems, SECL,
What is cut-off rate?
Total power capacity of india at present
what is interference
how brushed dc motor operating ?
What are the methods used to improve powerfactor ?
Why does The speed of motor used in elevator remain constant irrespective of load??
why we have to particulary use ACB for below ratings,even available of MCB,MCCB with that range ?
2 Answers QRG Health City, Siemens,
We have ONLINE UPS 15KvA (3PHASE 440V I/P,3PHASE O/P,440V) I want to step down from 440 to 220 V What to do. Pl. suggest with specification.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)