Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


One Township having 850 house and each house load is 2.2KW
single phase & 5HP 3 Phase motors of 10 Nos .Who can
calculate 11 KV transformer
capacity .dilip_bhasker@yahoo.co.in



One Township having 850 house and each house load is 2.2KW single phase & 5HP 3 Phase motors o..

Answer / naresh

The total lighting load of the township is 1870KW and motor
load is 50HP.

We have to load the transformer upto 80percent of
its KVA rating. Because the average power factor has been
taken as 0.8 and to avoid the over loading problem.

So for the township the transformer capacity is as follows.
24x100KVA + 1x63KVA or 15x160KVA + 1x63KVA

Multiple transformers provided instead of few high
capacity transformers to avoid low voltage problem at tail
end.

Is This Answer Correct ?    2 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

Can I use measuring current transformers in protection purposes?

7 Answers  


what is rated current and operating current?

1 Answers  


Distinguish between neutral earthing and equipment earthing?

7 Answers  


What is IGBT?Where it is used? What is the difference between IGBT and Thyristor?

5 Answers   AC, Formo Plastic, HBL Power Systems, SECL,


What is cut-off rate?

0 Answers  


Total power capacity of india at present

8 Answers   Bhel,


what is interference

1 Answers   L&T,


how brushed dc motor operating ?

0 Answers  


What are the methods used to improve powerfactor ?

6 Answers  


Why does The speed of motor used in elevator remain constant irrespective of load??

1 Answers  


why we have to particulary use ACB for below ratings,even available of MCB,MCCB with that range ?

2 Answers   QRG Health City, Siemens,


We have ONLINE UPS 15KvA (3PHASE 440V I/P,3PHASE O/P,440V) I want to step down from 440 to 220 V What to do. Pl. suggest with specification.

1 Answers   ARDE,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)