One Township having 850 house and each house load is 2.2KW
single phase & 5HP 3 Phase motors of 10 Nos .Who can
calculate 11 KV transformer
capacity .dilip_bhasker@yahoo.co.in
Answer / naresh
The total lighting load of the township is 1870KW and motor
load is 50HP.
We have to load the transformer upto 80percent of
its KVA rating. Because the average power factor has been
taken as 0.8 and to avoid the over loading problem.
So for the township the transformer capacity is as follows.
24x100KVA + 1x63KVA or 15x160KVA + 1x63KVA
Multiple transformers provided instead of few high
capacity transformers to avoid low voltage problem at tail
end.
| Is This Answer Correct ? | 2 Yes | 3 No |
What is the function of an Auto reclosure relay. How does it work??
the parts of transformers ?
1 Answers Bhel, Facility management,
why eee branch?
How to covert the ac to dc and how to control the dc output?
What is the knee point voltage of CT-100/5,15VA,5P20 ?
what are the interview question asked in wind mill about electrical
For a CT the number of turns in the primary winding is.........
A synchronous motor is operating at a leading power factor .if the applied voltage is decreases ,(the excitation remains constant ) ,the motor current a)increases b) decreases c)remains same d) none of these
check list for anuval maintatince check list of oil transforms
can we use only a isolator in the subtation..
Difference between On Line capacitor and Station Type capacitor.
why inductance is not present in a incandescnt lamp?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)