Answer / kapil narayanrao bahadure
In any Industry, voltage level either 3.3kV or 6.6KV its
not chose the motor ratings.voltage level in any industry
depend upon total load of industry.firstly total load of
industry consideration & after voltage level consider.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / kunal
for cost consideration of motor: It is tradeoff.. now if
high voltage rating is selected less current will flow for
same load . this will save costs on copper but at the same
time cost of insulation will increase. .....if lower voltage
is chosen then higher currents will result for same load. so
higher cost of copper but reduced cost of insulation.
for consideration of voltage for industry depends on the
load. and if heavy loads are present usually higher volatges
are chosen as losses due to current are far more.
MW rated motors will always be run on higher voltages.
higher the better.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / veena
To choose the voltage level for any Load two factors has to
be considered one is the Total load and the distance of
transmission line .There is a formula to calculate the
economic transmission voltage
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / rocks
6.6kv line.it also depend on the rating ot the motor that
is if high motor rating the vtg drop is siginifently more
than low motor rating.hence 606kv line is morepreffered in
industry
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / parth rawal
voltage level chosen 3.3kv due to insulation consideration
| Is This Answer Correct ? | 0 Yes | 2 No |
Which state of India had first started power reforms?
what is the reason for harmonics introduced in the line
Motor also having losses, we call KW rating. In transformer and generator having losses but we call KVA Rating why?
how to select a breaker (MCB,MCCB,ELCB) for 18.5 kw, 3 ph. 480 v, 60 hz induction motor?
how to design step down 12 V, 1mA small transformer from 220 V AC? Because according to VI relation and power transfer it results bulky...
Transformer TTR test procedure
A cotter joint is generally used to transmit
What is the rating of circuit breaker needed for 300 KVA load in 33 KV supply line in a transformer of 33 KV / 415 Volt ?
How can remove the jerks on genretor due to remov or connecting the load ?
what is the load amp of a 2 hp single phase motor?
tell me some type of questions throught which i can prepare for exam and do my best
If a generator of generating station produces 100MW rated output then what will be the rating of the step-up transformer connected to it?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)